Results 1 to 7 of 7
04-02-2012, 05:16 PM #1
Hitachi dc inverter service manual
HI Guys,
ANYONE OUT THERE GOT A MANUAL FOR THE HITACHI RAC50YH6 PLEASE.
aPPRECIATED.
04-02-2012, 05:26 PM #2
Re: Hitachi dc inverter service manual
got one for the rac50 wx8 and a rac 60yh7 and a rac50dh7
05-02-2012, 03:50 AM #3
ive got them for all the australian models. ie RAS/RAC50YHA1 & RAS/RACYHA2
not sure how different they would be to your YH6
05-02-2012, 03:11 PM #4
Can try the closest manual if fine for you.Can I pm to you or ? How you wish.
Kindly update.
05-02-2012, 04:37 PM #5
Have a look through these.
https://rapidshare.com/files/1365601...H7_PM0372E.pdf
https://rapidshare.com/files/2874978...8_TC0783EF.pdf
https://rapidshare.com/files/6162017...H7_PM0467E.pdf
Cheers
StuTool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
05-02-2012, 08:56 PM #6
Hi Stufus,
Incredible as always man.Always got me out of mud !
Thanks for the manuals,one of them is nearly identical,so can manage to test.
I am reading an output of 35v from the inverter card to the indoor unit.So it must be the indoor card,but will check electronics wise tomorrow.Thanks again Stufus.
I also thank Assailiant for attemp of help.I do thanks just as if have used your max ;D
05-02-2012, 09:55 PM #7
No worries mate
Cheers