Mitsubishi RP200YHA-PEARP200GA ducted system
Guys
Have inherited 4 of the above systems in a maintenance contract. The systems are cooling an IT room (wrong equipment), the client has had 4 x steam humidifiers installed to up the humidity.
Does anybody know if the equipment can be modified so we can get more sensible cooling and negate the steamers.
-
06-02-2012, 06:42 AM #2
Re: Mitsubishi RP200YHA-PEARP200GA ducted system
Solve the Undersized units. Sensible load is too big for these system. In fact IT room should use PFD instead.