    30RA Scroll AIR – Water Chiller (30RA 160A)



    Hi everybody,
    Present, I used the Chiller "30RA Scroll AIR – Water Chiller (30RA 160A)"
    But I don't have the schematic of the this system. If you have them. Can you help me.
    I have a problem with this chiller.
    When I running this chiller then waiting about 30 second when this have 1 block run and only this block run.
    Remain 3 block not run.
    I don't know why.
    Can you help me.
    Thank you very much.



  2. #2
    Join Date
    Feb 2012
    Location
    england
    Age
    50
    Posts
    1
    Rep Power
    0

    Re: 30RA Scroll AIR – Water Chiller (30RA 160A)

    hi mate,i commission these carrier chillers regular,the 3rd compressor block on the controller is not in use on the 30RA,it only has 2 comps per circuit!

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: 30RA Scroll AIR – Water Chiller (30RA 160A)

    Attachment 8593
    Quote Originally Posted by deaklin View Post
    hi mate,i commission these carrier chillers regular,the 3rd compressor block on the controller is not in use on the 30RA,it only has 2 comps per circuit!
    Hi deaklin.
    I suspect you know far more about these than me.
    However I have to dispute the 2 comps statement as there is a 3 comp per circuit version.
    In fact reading my own attachment it would appear the 160 is indeed 2 +2 comps?
    That does not mean that Vanpu has such of course.

    Grizzly
    Last edited by Grizzly; 01-02-2012 at 07:19 PM.

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: 30RA Scroll AIR – Water Chiller (30RA 160A)

    Some RA's have 4 comps per circuit I would need full model to be sure though

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 30RA Scroll AIR – Water Chiller (30RA 160A)

    Or pick up some details from here...

    http://eto.carrier.com/lit.asp
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Feb 2012
    Location
    Memhitech
    Age
    35
    Posts
    3
    Rep Power
    0

    Re: 30RA Scroll AIR – Water Chiller (30RA 160A)

    Hi everybody,
    Thank you for help me.
    I'm sorry. It have 2 circuit unit: circuit A and circuit B. But each circuit have 2 compressor.
    I think it have problem at the Pro – Dialog control.
    Tomorrow, The chiller only run 1 compressor.
    Today, I tried again. First, the chiller run have 2 compressor then auto shutdown.When I try again its have error then I reset this error and run the chiller again. Its run good (have 4 compressor run)

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: 30RA Scroll AIR – Water Chiller (30RA 160A)

    Hi vanphu.
    The fault you reset may be the clue to what is wrong, what was it?
    Grizzly

  8. #8
    Join Date
    Feb 2012
    Location
    Memhitech
    Age
    35
    Posts
    3
    Rep Power
    0

    Re: 30RA Scroll AIR – Water Chiller (30RA 160A)

    Hi Grizzly,
    Now, The chiller activities good.
    All compressor activities and its not error.