01-02-2012, 08:32 AM #1
30RA Scroll AIR – Water Chiller (30RA 160A)
Hi everybody,
Present, I used the Chiller "30RA Scroll AIR – Water Chiller (30RA 160A)"
But I don't have the schematic of the this system. If you have them. Can you help me.
I have a problem with this chiller.
When I running this chiller then waiting about 30 second when this have 1 block run and only this block run.
Remain 3 block not run.
I don't know why.
Can you help me.
Thank you very much.
-
01-02-2012, 12:37 PM #2
Re: 30RA Scroll AIR – Water Chiller (30RA 160A)
hi mate,i commission these carrier chillers regular,the 3rd compressor block on the controller is not in use on the 30RA,it only has 2 comps per circuit!
-
01-02-2012, 07:16 PM #3
Re: 30RA Scroll AIR – Water Chiller (30RA 160A)
Attachment 8593Hi deaklin.
I suspect you know far more about these than me.
However I have to dispute the 2 comps statement as there is a 3 comp per circuit version.
In fact reading my own attachment it would appear the 160 is indeed 2 +2 comps?
That does not mean that Vanpu has such of course.
GrizzlyLast edited by Grizzly; 01-02-2012 at 07:19 PM.
-
01-02-2012, 07:44 PM #4
Re: 30RA Scroll AIR – Water Chiller (30RA 160A)
Some RA's have 4 comps per circuit I would need full model to be sure though
-
01-02-2012, 08:34 PM #5
Re: 30RA Scroll AIR – Water Chiller (30RA 160A)
Or pick up some details from here...
http://eto.carrier.com/lit.aspBrian - Newton Abbot, Devon, UK
Retired March 2015
-
02-02-2012, 01:22 AM #6
Re: 30RA Scroll AIR – Water Chiller (30RA 160A)
Hi everybody,
Thank you for help me.
I'm sorry. It have 2 circuit unit: circuit A and circuit B. But each circuit have 2 compressor.
I think it have problem at the Pro – Dialog control.
Tomorrow, The chiller only run 1 compressor.
Today, I tried again. First, the chiller run have 2 compressor then auto shutdown.When I try again its have error then I reset this error and run the chiller again. Its run good (have 4 compressor run)
-
02-02-2012, 06:06 AM #7
Re: 30RA Scroll AIR – Water Chiller (30RA 160A)
Hi vanphu.
The fault you reset may be the clue to what is wrong, what was it?
Grizzly
-
02-02-2012, 06:37 AM #8
Re: 30RA Scroll AIR – Water Chiller (30RA 160A)
Hi Grizzly,
Now, The chiller activities good.
All compressor activities and its not error.
But I don't know the tomorrow what problem?