    LG split tripping breaker



    Hi all been called to a LG split system it's a floor mount indoor unit and the outdoor has 2 compressors. When I arrived power was off so immediately gained access to distribution board and breaker was tripped. Immediately thought compressor was fault. Reset breaker and unit started and ran fine loaded up the system and ran it on full load both comps in everything seemed fine. Checked comp.amps all ok. Watched the unit cycle on and off for good hour no problem. Was just getting customer to sign service report and the system tripped breaker. Reset and it tripped again before I got to outdoor by now it was pitch dark so put in some temp cooling and left. If it was the comps causing the trip then why would it run for good hour and half I'm thinking it must be comp or contactor as if it was the capacitor or defective wires then it would of tripped sooner. Sorry don't have model numbers but can get if need be. What you think am I going in the right direction or missing something. The breaker is a 32 amp c type which should be ok for the unit.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: LG split tripping breaker

    earth leakage, or if the neutral in the isolator is switched,that can cause problems, ensure the neutral is on the terminal block instead of the switched pole,also circuit breakers can get warm and weaker- inverters should be on a d type breaker(motor rated)

  3. #3
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: LG split tripping breaker

    Quote Originally Posted by install monkey View Post
    ......... inverters should be on a d type breaker(motor rated)
    Why is that?

  4. #4
    Join Date
    Jun 2011
    Location
    Australia
    Posts
    47
    Rep Power
    0

    Re: LG split tripping breaker

    Hi. Have a look rated amps equals accual amps. A faulty cap can cause this problem. The insulation resistance is ok of compresser and unit. I have had a faulty circuit breaker trip after a given time but generally within a few minutes. I hope this helps.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: LG split tripping breaker

    check for water in the isolator too

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: LG split tripping breaker

    so when ur daughters pet hamster nibbles through the supply it get char grilled- teach it not to chew wires again
    Quote Originally Posted by r.bartlett View Post
    Why is that?

  7. #7
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: LG split tripping breaker

    Ok guys cheers

    But if it was a faulty cap then surely it would trip almost straight away same for water in the isolator surely it wouldn't run for a good hour with no problem cycling on and off at full load quite happily. Something must be steadily getting hotter. After the unit ran for a good hour it tripped breaker and when reset only ran for few minutes so can only think that when I arrived at site whatever's causing the trip had cooled and took a good hour to heat up to the point that it caused the breaker to trip

  8. #8
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: LG split tripping breaker

    Megger the comps sounds like one's on it's last legs.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  9. #9
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: LG split tripping breaker

    if its a b series check the crank heaters if its a c series check the insulated jacket for water around the terminal blocks if its a d series the loom rubs on the eev and on full volts ie after run down its enough to dump the breaker alsowe have been always told tpye c breakers on motor rated we only use type d on heater mats in the c rooms we always fit fridge kit on type c breakers is this correct we have never had any problems ta charlie

  10. #10
    Join Date
    Jul 2006
    Location
    Reading
    Posts
    5
    Rep Power
    0

    Re: LG split tripping breaker

    hi, not sure if you have solved your problem, but we have had a similar problem recently. are the breakers on an rcd breaker? after a couple of visits, and lots of finger pointing, it turns out the sparkys had fed our condensers off of an rcd board. they changed the board, no problems since!

    kev

  11. #11
    Join Date
    Oct 2011
    Location
    new zealand
    Posts
    22
    Rep Power
    0

    Re: LG split tripping breaker

    insulation test the feed cable as i have struck that before and it would trip after the cable warms up due to damage from mice

  12. #12
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: LG split tripping breaker

    Second compressor was throwing breaker when I went back to site compressor was throwing breaker straight away must of been getting a bit tight but now is well and truly seized priced to replace. Got the job to repair leak on its sister unit which I did but found a secondary fault restriction causing very low suction pressure switched modes gave reversing valve a knock put back into cooling and unit worked fine for about 8 hrs then stopped again back at zero bar suction fun times