    leak in ammonia plant



    HI EVERY BODY,One day my ammonia plant running smoothly with good temperture then suddenly their is leak in heatexchanger ammonia start to come out to atmospere then i check but i cannot find why this happen can any help me to know how this one happen . thank you all



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: leak in ammonia plant

    could you give us more information about you system and your heat exchanger. to find leaks in NH3 is very easy ((smelling )) is a best way .,

  3. #3
    Join Date
    May 2007
    Location
    Pennsylvania
    Age
    51
    Posts
    113
    Rep Power
    17

    Re: leak in ammonia plant

    Sulphur sticks are handy to catch very small pinhole leaks but it's very rare to get a leak on an ammonia system without corrosion unless you are leaking at a flanged joint of some type.

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: leak in ammonia plant

    Could it be that you had a pressure relief valve, opened releasing NH3, then resetting.

  5. #5
    Join Date
    Jul 2008
    Location
    Singapore & Malaysia
    Age
    77
    Posts
    30
    Rep Power
    0

    Re: leak in ammonia plant

    Best method to check tube leakage, if nonferrous material use Eddy Current Tubing Examination and if ferrous material use Remote Field Eddy Current (RFT)/Internal Rotary Inspection System (IRIS) as such NDT methods could solve your problem.
    If you test 100% of the tubes than you will know which tube having wall thickness loss and the percent of wall loss and take quick action to plug off the defect tubes, in anticipation of tube failure.

  6. #6
    Join Date
    Mar 2012
    Location
    United Kingdom
    Posts
    17
    Rep Power
    0

    Re: leak in ammonia plant

    Could you give better information surrounding your refrigeration plant?

    I.e. Make of unit, type of heat exhanger (PHE/Shell and tube)