    Jan 2011
    India
    7
    Effect of Suction Super heat in flooded evaporator using Ammonia
    Dear all,
    hello
    i want to ask what is the effect of Suction Superheat in flooded evaporator using ammonia ?
    does it same as in case of dry evaporator ?
    how to handle it if i have a manual expansion valve ?
    3,355
    Re: Effect of Suction Super heat in flooded evaporator using Ammonia
    pushcar, no superheat on this type of system.
    Liquid recirculation or overfeed has a rate of example 4 to 1
    4 kg of refrigerant sent to evaporator, 3 comes back as liquid & 1 kg converted to saturated gas.
    No real superheat is measured, only air on/off temps as per design or if surge drum, correct level is achieved
    by approx liquid feed solonoid on 70% of the time under full load conditions. Set manual expansion valve to meet above requirments.
    Jul 2006
    865
    There was a really good thread on this sometime back.
    http://www.refrigeration-engineer.co...hlight=brining
    US Iceman wrote a paper on this. One of the best I have read. It is on the Internet, and a link is probably in the thread. I have it on my computer and will find it sooner or later.
    3,355
    Quote Originally Posted by NH3LVR View Post
    Some of it starts from post number 97 on above thread.