Results 1 to 14 of 14
Thread: Ice cream display case problems.
15-01-2012, 01:15 PM #1
Ice cream display case set at -13.5Stock at one end very hard, Other end very soft. All fans running in The same direction. 2 defrosts per day for 15 minsTo defrost fallen icecream. Why is the stock varying in temp so much?
15-01-2012, 05:43 PM #2
Re: Ice cream display case problems.
faulty stat,compressor overheating or short of gas
15-01-2012, 06:33 PM #3
is it a straight case or a multideck version
15-01-2012, 08:21 PM #4
It is a straight case, full sight glass at all times, if it hadA faulty stat wouldn't we still see a uniform temp in the case?Has worked previously.
15-01-2012, 08:54 PM #5
Is half of the evap coil iced up ?
when you say straight case? what type of freezer is it?
hot gas defrost? elec defrost?
is the case defrosting correctly?
defrost time seems short for 2 defrosts per day, what is the defrost term temp set to?your only as good as your last job
15-01-2012, 09:06 PM #6
Air flow maybe
Can the air fully circulate the load, nothing stacked on the floor or against the wallIf the World did not Suck, We would all fall off !
15-01-2012, 09:13 PM #7
are the defrost heaters staying on? contactor/relay welded!!
16-01-2012, 08:08 PM #8
first step is lower the setpoint minus 13.5 aint enough for icecream
17-01-2012, 08:55 PM #9
Are the brands of ICe Cream different from end to end. I have always seen that higher end ice cream is harder to freeze
17-01-2012, 11:41 PM #10
Holding temp for ice cream is -20'C, storage temps between -29 and -26'C
17-01-2012, 11:50 PM #11
around -13 its easier to scoop up as opposed to the solid block in ur own freezer
18-01-2012, 08:14 PM #12
cant agree there install minus 13 thats to soft for all our customers mate the problem set at minus 13 it aint cutting in untill minus 11 and it aint running long enough to ice the evap all the way thats why it may have such a temp diff in chamber set to minus 18 and let it settle most of the isa and framecs only df twice a day and the reason for high end ice cream requires more freezing is it useually contains more sugar or alcohol
19-01-2012, 01:27 PM #13
Heat source or direct sunlight at one end?
20-01-2012, 01:03 AM #14
what is your superheat