    leak detection agent



    got some leaks [small] on a cold store 4 evaps r22 100 hp grasso,want to add some agent to try to locate pretty sure the leaks are on evaps but access is dificult traffic etc was hoping to try to speed up the process any reccomendations.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: leak detection agent


  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: leak detection agent

    Hi Cadwaladr.
    I have used spectroline on coldstore evaps to great success in the past, particularly on a R22 system.

    The UV Lamps can be shone on the evaps from a safety cage and in a low light any leaks are well indicated.
    How happy your customer may be when his evap coils are proven to be sieves, I am not so sure about?
    I even made up a dosing fitting for adding it via a Grasso oil gauge line.
    Much cleaner than some methods of adding the spectroline. As many have said before you need to be ultra clean when adding it or your plant room, equipment and kit glow green.
    Cheers Grizzly.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: leak detection agent

    Iif you want to use it, I can send you mine, I dont use it any more,

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: leak detection agent

    use spectroline as a last resort as every time u work on that system ur gonna get ur gauge lines and yourself covered in dye, it is handy though

  6. #6
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: leak detection agent

    thanks for the offer chemi but we are not close,yes i know that this stuff will go everywhere if care is not taken and as for the evaps looking like radioactive isotopes that is the chance worth taking the plant is due a refit but the money is hiding behind the common sense door and will not come out,we dont have a major leak but with the cost of this stuff r22r we need to nail the leak,on the adaptor we have a selection of spares so could make one but we can put it in via a close access point to the evap piping without entering cold store thanks grizzly yours the man who will have no need for a high viz jacket soon lol.