Results 1 to 10 of 10
  1. #1
    Join Date
    Jan 2012
    Location
    Namibia
    Posts
    5
    Rep Power
    0

    Cool carrier compressor problems



    Hi everyone

    I'm new to this site but from what ive read so far it sounds like you guys know your stuff. Ive got a carrier reefer(69NT40-511-312) with a recipient compressor that stays in a vacuum and doesnt reach its set point, i think it mite be the txv that is faulty but any other advise would be greatly appreciated.

    Set Point -20
    Return temp -0.2
    Supply Temp -16,7
    SMV 100% Open

    Thanks in advance
    -20



  2. #2
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    347
    Rep Power
    18

    Re: carrier compressor problems

    no air flow, so blocked evaporator coil or fan clutch not working so no drive to fan in back, try these first.
    if you take off the evaporator panel you'll see a big ice formation
    Last edited by gravy258; 10-01-2012 at 06:34 AM.

  3. #3
    Join Date
    Nov 2009
    Location
    Canada
    Posts
    123
    Rep Power
    15

    Re: carrier compressor problems

    have you physically check the SMV may say100% but could be stuck closed

  4. #4
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    347
    Rep Power
    18

    Re: carrier compressor problems

    he has a very big temp difference across the coil, so i'm thinking simple stuff first

  5. #5
    Join Date
    Jan 2012
    Location
    Namibia
    Posts
    5
    Rep Power
    0

    Re: carrier compressor problems

    thanks for input guys, but after further investigation i found that the txv bulb was broken. replaced faulty part, reefer running fine now.

    Anybody know where i can download th new 5#54 carrier software, the port i work at is not a registered carrier service centre so i cant get the software from carriers site?

  6. #6
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: carrier compressor problems

    I work with a compressor manufacturing company............... Anytime anything goes wrong other than with compressor , customers relate it to compressor faulty , not working ,defective etc . I thought it is a local phenomena but appears to be a common .

  7. #7
    Join Date
    Jan 2012
    Location
    Namibia
    Posts
    5
    Rep Power
    0

    Re: carrier compressor problems

    No guy, like i said the TXV was faulty. Nothing wrong with the compressor, i wasnt even hinting at that...

  8. #8
    Join Date
    Dec 2010
    Location
    Philippines
    Age
    33
    Posts
    30
    Rep Power
    0

    Re: carrier compressor problems

    me me me me i have problem the suction section of my compressor is icing heavier and heavier as time past when the unit is running what is the probable cause of this????

  9. #9
    Join Date
    Dec 2010
    Location
    Philippines
    Age
    33
    Posts
    30
    Rep Power
    0

    Re: carrier compressor problems

    me me me me i have problem the suction section of my compressor is icing heavier and heavier as time past when the unit is running what is the probable cause of this????

  10. #10
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    347
    Rep Power
    18

    Re: carrier compressor problems

    Quote Originally Posted by -20 View Post
    No guy, like i said the TXV was faulty. Nothing wrong with the compressor, i wasnt even hinting at that...
    rom the threa

    apart from the thread title..