    Centrifugal chiller.



    Hello Mates,

    Could someone tell me what the lowest water outlet temperature in a centrifugal chiller is?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Centrifugal chiller.

    what make and model

  3. #3
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Centrifugal chiller.

    Quote Originally Posted by install monkey View Post
    what make and model
    Carrier, York, Trane...

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Centrifugal chiller.

    depends on the system design/application

  5. #5
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Centrifugal chiller.

    Just pure water. How low we can cool water down with a R134A centrifugal chiller?

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Centrifugal chiller.

    carrier 19xr Evaporator 19XR Minimum Maximum
    Evaporator entering water temperature* °C 6 17
    Evaporator leaving water temperature* °C 3.3 10
    Condenser (water-cooled) 19XR Minimum Maximum
    Condenser entering water temperature* °C 16 35
    Condenser leaving water temperature* °C 13.3 44
    *
    For application requiring brine operation, contact Carrier s.a. for unit selection

  7. #7
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Centrifugal chiller.

    Hi
    wouldnt try to go lower than 5 degc/.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  8. #8
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Centrifugal chiller.

    AS ABOVE
    I wouldn't take untreated water below 4-5c as Ice crystals will start to form ,Which could get messy quickly.
    Cheers
    Stu
    Last edited by stufus; 08-01-2012 at 09:29 PM. Reason: Goshen got there first
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Centrifugal chiller.

    york lchmChilled Water Leaving Temperature : R22 & R134a models : 4.0 °C 10 °C
    R 407C models : 6.0 °C 10 °C
    Chilled Glycol Leaving Temperature : R22 & R134a models : - 6 °C 10 °C
    R 407C models : - 2 °C 10 °C
    WATER /
    Chilled Liquid Temperature Range through Cooler : 3.3 °C 8 °C
    GLYCOL
    Standard Condenser R22 models : 30 °C 41 °C
    SYSTEMS
    Liquid Leaving Temperaure : R134a models : 30 °C 55 °C
    R407C models : 30 °C 35 °C

  10. #10
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Centrifugal chiller.

    Quote Originally Posted by install monkey View Post
    carrier 19xr Evaporator 19XR Minimum Maximum
    Evaporator entering water temperature* °C 6 17
    Evaporator leaving water temperature* °C 3.3 10
    Condenser (water-cooled) 19XR Minimum Maximum
    Condenser entering water temperature* °C 16 35
    Condenser leaving water temperature* °C 13.3 44
    *
    For application requiring brine operation, contact Carrier s.a. for unit selection
    It means that for your example the lowest water temperature is 3,3 deg. C? Is it the limit? Could we go lower? What limits the lowest water temperature? Evaporation temperature? Evaporator construction?

  11. #11
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Centrifugal chiller.

    I still wouldn't run it down below 4-5c
    Cheers
    Stu
    Quote Originally Posted by install monkey View Post
    york lchmChilled Water Leaving Temperature : R22 & R134a models : 4.0 °C 10 °C
    R 407C models : 6.0 °C 10 °C
    Chilled Glycol Leaving Temperature : R22 & R134a models : - 6 °C 10 °C
    R 407C models : - 2 °C 10 °C
    WATER /
    Chilled Liquid Temperature Range through Cooler : 3.3 °C 8 °C
    GLYCOL
    Standard Condenser R22 models : 30 °C 41 °C
    SYSTEMS
    Liquid Leaving Temperaure : R134a models : 30 °C 55 °C
    R407C models : 30 °C 35 °C
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  12. #12
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Centrifugal chiller.

    You are limited by your medium=water....Ice starts to form around 4c
    Cheers
    Stu
    Quote Originally Posted by Jacek View Post
    It means that for your example the lowest water temperature is 3,3 deg. C? Is it the limit? Could we go lower? What limits the lowest water temperature? Evaporation temperature? Evaporator construction?
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Centrifugal chiller.

    not if u add salt! haha

  14. #14
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Centrifugal chiller.

    Quote Originally Posted by install monkey View Post
    york lchmChilled Water Leaving Temperature : R22 & R134a models : 4.0 °C 10 °C
    R 407C models : 6.0 °C 10 °C
    Chilled Glycol Leaving Temperature : R22 & R134a models : - 6 °C 10 °C
    R 407C models : - 2 °C 10 °C
    WATER /
    Chilled Liquid Temperature Range through Cooler : 3.3 °C 8 °C
    GLYCOL

    Standard Condenser R22 models : 30 °C 41 °C
    SYSTEMS
    Liquid Leaving Temperaure : R134a models : 30 °C 55 °C
    R407C models : 30 °C 35 °C

    We are talking about centrifugal chillers...

  15. #15
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Centrifugal chiller.

    Then it's not "pure water" , could always p1ss in it.
    Cheers
    Stu
    Quote Originally Posted by install monkey View Post
    not if u add salt! haha
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  16. #16
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Centrifugal chiller.

    Quote Originally Posted by goshen View Post
    Hi
    wouldnt try to go lower than 5 degc/.
    good luck
    Why? What is/are the limits?

  17. #17
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Centrifugal chiller.

    Hi
    it is simple as water will freeze at 0 degc, but as said above crystals start to form at 2-3degc
    this will lead to evap failure!
    wouldnt go there !
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  18. #18
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Centrifugal chiller.

    Quote Originally Posted by goshen View Post
    Hi
    it is simple as water will freeze at 0 degc, but as said above crystals start to form at 2-3degc
    this will lead to evap failure!
    wouldnt go there !
    But if you are the evaporation temperature above +1 deg. C? We could maintain the evap temp above +1 deg. C...

  19. #19
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Centrifugal chiller.

    The type of chiller is irrelevant !!!
    WATER IS WATER ! operating below 4c is dangerous territory with an expensive piece of kit
    Cheers
    Stu
    Quote Originally Posted by Jacek View Post

    We are talking about centrifugal chillers...
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  20. #20
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Centrifugal chiller.

    If you want to go below 5c you need to add a brine/glycol solution if you don't your unit will fail you
    Can not get the water below 5 without an evaporation temp of 0c or below. Get yourself a piece of
    Copper tube fill it with water seal both ends and put it in a freezer then you will see the results for
    Yourself
    As mentioned make/model machine is it

  21. #21
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Centrifugal chiller.

    Hi Jacek

    am with the other members who have replied here... 1*c is way too low

    when commissioning i lock out the set point at 6*c and set ice/freeze protection to 4*c

    also if evaporating at 1*c the only way the water will reach that temp is if you have no flow !

    why do you require 1*c ? what are you cooling and what is the problem ?

    chillerman
    If the World did not Suck, We would all fall off !

  22. #22
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Centrifugal chiller.

    Quote Originally Posted by chillerman2006 View Post
    Hi Jacek

    am with the other members who have replied here... 1*c is way too low

    when commissioning i lock out the set point at 6*c and set ice/freeze protection to 4*c

    also if evaporating at 1*c the only way the water will reach that temp is if you have no flow !

    why do you require 1*c ? what are you cooling and what is the problem ?

    chillerman
    If we maintain the evap temp at +1 deg C, we could get the water temp at 2-3 deg. C (as goshen said). What is the problem? Is it a problem to maintain so low dt between evap temp and water outlet temp?

    My question was the general one - how low we could go down with the "pure" water temperature using a ***** chiler...?

  23. #23
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Centrifugal chiller.

    Jacek

    you need to protect that evap/vessel

    so normally you have ice/freeze protection set to 4*c and the low pressure switch set to 0*c

    what would you set these to if you lowered the setpoint ?
    If the World did not Suck, We would all fall off !

  24. #24
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Centrifugal chiller.

    You can have close to 0C easily if you use the right evaporator "jester chenson plate" or the like, you can use a closed heat exchanger, shell and tube or plate pack, but extreme care is required. very high water velocities and volumes, super control on suction pressures and a lot of other safeties.
    In these case temp drop of water is minimal due to the high flow rates.

  25. #25
    Join Date
    Oct 2011
    Location
    usa
    Posts
    2
    Rep Power
    0

    Re: Centrifugal chiller.

    a york yk can go to 36 degrees F with smart freeze enabled

  26. #26
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Centrifugal chiller.

    Quote Originally Posted by spinning wheel View Post
    a york yk can go to 36 degrees F with smart freeze enabled
    What's that?

  27. #27
    Join Date
    Jul 2007
    Location
    LIbya
    Age
    58
    Posts
    72
    Rep Power
    17

    Re: Centrifugal chiller.

    Hi jacek
    the specific volume for water will increase at 4c so inlet water temperature should not reach to 4c.

  28. #28
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Centrifugal chiller.

    Smart freeze is a York control strategy on the their YK/YS chillers that allows the leaving water temp to be set as low as 2.2c .However programming the parameters to do this needs to be done by someone who knows what they are at.
    The software constantly monitors the sensors and temperatures to avoid freeze up.
    It's a big song and dance for the sake of 2.5c or a drop of anti freeze.
    www.johnsoncontrols.co.uk/...chillers/yk/.../OI-EN-YK.pdf
    Cheers
    Stu
    Quote Originally Posted by Jacek View Post
    What's that?

  29. #29
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Centrifugal chiller.

    Why do you want to use pure water as opposed to an anti freeze?
    Mostly found in Oxfordshire, UK :)

  30. #30
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Centrifugal chiller.

    Quote Originally Posted by Jacek View Post
    Carrier, York, Trane...
    Quote Originally Posted by Jacek View Post
    My question was the general one - how low we could go down with the "pure" water temperature using a ***** chiler...?
    The general answer for a packaged chiller 'carrier, york, trane' is 6*c

    Quote Originally Posted by mad fridgie View Post
    You can have close to 0C easily if you use the right evaporator "jester chenson plate" or the like, you can use a closed heat exchanger, shell and tube or plate pack, but extreme care is required. very high water velocities and volumes, super control on suction pressures and a lot of other safeties.
    In these case temp drop of water is minimal due to the high flow rates.
    a bespoke system as above would require a 'mad fridgie' supply and fit plus regular tlc from a 'magoo'

    Quote Originally Posted by spinning wheel View Post
    a york yk can go to 36 degrees F with smart freeze enabled
    if you can supply the flow rates

    Quote Originally Posted by monkey spanners View Post
    Why do you want to use pure water as opposed to an anti freeze?
    maybe cost £/$... heat transfer drops and cooling costs rise when anti-freeze is added
    If the World did not Suck, We would all fall off !

  31. #31
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Centrifugal chiller.

    Hello,

    Could someone tell me what the highest pressure ratio (evaporation temperature/condensing) for a R134a centrifugal chiller? Conditions are, for instance: evaporation temperature = 0-1'C, condensing temperature = "?" (what is the highest possible).

    Tnaks in advance for input.

  32. #32
    Join Date
    Dec 2008
    Location
    pa
    Posts
    1
    Rep Power
    0

    Re: Centrifugal chiller.

    You are talking about the lift and that will be in the design of the chiller.

  33. #33
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Centrifugal chiller.

    Quote Originally Posted by DITAW View Post
    You are talking about the lift and that will be in the design of the chiller.
    I am asking about that... What is the highest possible, let's say, lift?