    Hello Mates,
    Could someone tell me what the lowest water outlet temperature in a centrifugal chiller is?
    manchester
    5,639
    Re: Centrifugal chiller.
    what make and model
    Nov 2006
    Poland
    91
    what make and model
    Carrier, York, Trane...
    manchester
    5,639
    depends on the system design/application
    Nov 2006
    Poland
    91
    Just pure water. How low we can cool water down with a R134A centrifugal chiller?
    manchester
    5,639
    carrier 19xr Evaporator 19XR Minimum Maximum
    Evaporator entering water temperature* °C 6 17
    Evaporator leaving water temperature* °C 3.3 10
    Condenser (water-cooled) 19XR Minimum Maximum
    Condenser entering water temperature* °C 16 35
    Condenser leaving water temperature* °C 13.3 44
    For application requiring brine operation, contact Carrier s.a. for unit selection
    Apr 2009
    israel
    778
    wouldnt try to go lower than 5 degc/.
    good luck
    Jun 2009
    Lusk , Dublin
    1,115
    AS ABOVE
    I wouldn't take untreated water below 4-5c as Ice crystals will start to form ,Which could get messy quickly.
    Stu
    manchester
    5,639
    york lchmChilled Water Leaving Temperature : R22 & R134a models : 4.0 °C 10 °C
    R 407C models : 6.0 °C 10 °C
    Chilled Glycol Leaving Temperature : R22 & R134a models : - 6 °C 10 °C
    R 407C models : - 2 °C 10 °C
    WATER /
    Chilled Liquid Temperature Range through Cooler : 3.3 °C 8 °C
    GLYCOL
    Standard Condenser R22 models : 30 °C 41 °C
    SYSTEMS
    Liquid Leaving Temperaure : R134a models : 30 °C 55 °C
    R407C models : 30 °C 35 °C
    Nov 2006
    Poland
    91
    It means that for your example the lowest water temperature is 3,3 deg. C? Is it the limit? Could we go lower? What limits the lowest water temperature? Evaporation temperature? Evaporator construction?
    Jun 2009
    Lusk , Dublin
    1,115
    I still wouldn't run it down below 4-5c
    Stu
    WATER /
    GLYCOL
    SYSTEMS
    Jun 2009
    Lusk , Dublin
    1,115
    You are limited by your medium=water....Ice starts to form around 4c
    Stu
    Quote Originally Posted by Jacek View Post
    manchester
    5,639
    not if u add salt! haha
    Nov 2006
    Poland
    91
    WATER /
    GLYCOL
    SYSTEMS
    We are talking about centrifugal chillers...
    Jun 2009
    Lusk , Dublin
    1,115
    Then it's not "pure water" , could always p1ss in it.
    Stu
    Nov 2006
    Poland
    91
    Quote Originally Posted by goshen View Post
    good luck
    Why? What is/are the limits?
    Apr 2009
    israel
    778
    it is simple as water will freeze at 0 degc, but as said above crystals start to form at 2-3degc
    this will lead to evap failure!
    wouldnt go there !
    Nov 2006
    Poland
    91
    wouldnt go there !
    But if you are the evaporation temperature above +1 deg. C? We could maintain the evap temp above +1 deg. C...
    Jun 2009
    Lusk , Dublin
    1,115
    The type of chiller is irrelevant !!!
    WATER IS WATER ! operating below 4c is dangerous territory with an expensive piece of kit
    Stu
    Jun 2009
    North East England
    712
    If you want to go below 5c you need to add a brine/glycol solution if you don't your unit will fail you
    Can not get the water below 5 without an evaporation temp of 0c or below. Get yourself a piece of
    Copper tube fill it with water seal both ends and put it in a freezer then you will see the results for
    Yourself
    As mentioned make/model machine is it
    Apr 2006
    55
    1,908
    30
    Hi Jacek
    am with the other members who have replied here... 1*c is way too low
    when commissioning i lock out the set point at 6*c and set ice/freeze protection to 4*c
    also if evaporating at 1*c the only way the water will reach that temp is if you have no flow !
    why do you require 1*c ? what are you cooling and what is the problem ?
    chillerman
    Nov 2006
    Poland
    91
    Quote Originally Posted by chillerman2006 View Post
    Hi Jacek
    chillerman
    If we maintain the evap temp at +1 deg C, we could get the water temp at 2-3 deg. C (as goshen said). What is the problem? Is it a problem to maintain so low dt between evap temp and water outlet temp?
    My question was the general one - how low we could go down with the "pure" water temperature using a ***** chiler...?
  23. #23
    Apr 2006
    55
    1,908
    30
    Jacek
    you need to protect that evap/vessel
    so normally you have ice/freeze protection set to 4*c and the low pressure switch set to 0*c
    what would you set these to if you lowered the setpoint ?
  24. #24
    Aug 2009
    New Zealand
    2,554
    You can have close to 0C easily if you use the right evaporator "jester chenson plate" or the like, you can use a closed heat exchanger, shell and tube or plate pack, but extreme care is required. very high water velocities and volumes, super control on suction pressures and a lot of other safeties.
    In these case temp drop of water is minimal due to the high flow rates.
  25. #25
    Oct 2011
    usa
    2
    a york yk can go to 36 degrees F with smart freeze enabled
  26. #26
    Nov 2006
    Poland
    91
    Quote Originally Posted by spinning wheel View Post
    What's that?
  27. #27
    Jul 2007
    LIbya
    58
    72
    Hi jacek
    the specific volume for water will increase at 4c so inlet water temperature should not reach to 4c.
  28. #28
    Jun 2009
    Lusk , Dublin
    1,115
    Smart freeze is a York control strategy on the their YK/YS chillers that allows the leaving water temp to be set as low as 2.2c .However programming the parameters to do this needs to be done by someone who knows what they are at.
    The software constantly monitors the sensors and temperatures to avoid freeze up.
    It's a big song and dance for the sake of 2.5c or a drop of anti freeze.
    www.johnsoncontrols.co.uk/...chillers/yk/.../OI-EN-YK.pdf
    Stu
    What's that?
  29. #29
    3,853
    Why do you want to use pure water as opposed to an anti freeze?
  30. #30
    Apr 2006
    55
    1,908
    30
    The general answer for a packaged chiller 'carrier, york, trane' is 6*c
    a bespoke system as above would require a 'mad fridgie' supply and fit plus regular tlc from a 'magoo'
    if you can supply the flow rates
    maybe cost £/$... heat transfer drops and cooling costs rise when anti-freeze is added
  31. #31
    Nov 2006
    Poland
    91
    Hello,
    Could someone tell me what the highest pressure ratio (evaporation temperature/condensing) for a R134a centrifugal chiller? Conditions are, for instance: evaporation temperature = 0-1'C, condensing temperature = "?" (what is the highest possible).
    Tnaks in advance for input.
  32. #32
    Dec 2008
    pa
    1
    You are talking about the lift and that will be in the design of the chiller.
  33. #33
    Nov 2006
    Poland
    91
    Quote Originally Posted by DITAW View Post
    I am asking about that... What is the highest possible, let's say, lift?