    Question Sporlan ORIT 15/20 installation tips



    Hello Everybody
    I have a question and I hope I posted in the right forum, I need to install some Sporlan ORIT 15/20 constant evaporator pressure valves, they require an high pressure pilot line, but the engine room is faraway from the installations, so I was wondering if I can use the liquid line before the expansion valves for this purpose.
    Can anybody help?
    Thank You very much.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Sporlan ORIT 15/20 installation tips

    Quote Originally Posted by Manual found at sporlan.com
    Externally Pilot Operated Valves – (S)ORIT-12, -15,and -20: Pressure Regulating Operation: These pilot operatedEPRs use high side pilot pressure to control the main valvepiston that regulates upstream/inlet pressure. The high sidepressure source allows this valve to be provided normallyopen. This allows the valve to be operated at minimal pres-sure drop to ensure maximum capacity by minimizing suc-tion line pressure losses. The high side pressure source mustmeet the following criteria to ensure optimum performanceof the pilot operated pressure regulating valve:

    • Only refrigerant vapor should be used as the high pres-sure supply source to the pilot valve.
    • The pilot supply line should be kept as short as possibleto minimize refrigerant condensation.
    So I would say that the answer to your question is NO, it does require a high pressure vapour supply...
    And further more, the selected valve is probably not suitable for your application.
    Sorry

  3. #3
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Sporlan ORIT 15/20 installation tips

    Thank You Viking

  4. #4
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Sporlan ORIT 15/20 installation tips

    I had read the part of the manual you are mentioning, I was hoping to hear from somebody that had took the risk of play with the word "should" present in the sentence

  5. #5
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Sporlan ORIT 15/20 installation tips

    Can anybody help suggesting which type/brand of valves should I use instead of the above mentioned valves (it seems they are not suitable for my needs) to regulate the evaporating pressure of some medium capacity evaporators? They are locate quite far away from the engine room so high pressure vapours are not an option, and regular Danfoss KVP line cannot cover the capacity I need....

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Sporlan ORIT 15/20 installation tips

    Look for KVP
    http://www.danfoss.com/NR/rdonlyres/.../PFH00A102.pdf

    Look at IRP
    http://www.actrol.com.au/WebSite.nsf/d974154241089741ca256cde000dcd9c/634211D12C8C906ECA256CE0000C62D4/$File/alcoregweb.pdf

    Try google sometimes, great help...

  7. #7
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Sporlan ORIT 15/20 installation tips

    Hi Chemicool, Thank You for your answer but, as I said in my post, KVP valves are too small for my needs, I had consider them and discarded the option, that's why I was asking for some more option...
    And also thank you for the suggestion of this "google" thing, I nver heard of it, I'll check it out... :-)

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Sporlan ORIT 15/20 installation tips

    Could you run two KVP valves parrallel to each other?
    Mostly found in Oxfordshire, UK :)

  9. #9
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Sporlan ORIT 15/20 installation tips

    Evapcoil,

    It's somewhat hard for us to come with suggestions when we haven't been given any of the design parameters apart from that the valves has to be installed far from the hot gas pipe...

    The best anybody can do under these circumstances is to point you towards the manufacturers information so that you who have the design criteria can make the selection.

  10. #10
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Sporlan ORIT 15/20 installation tips

    Quote Originally Posted by monkey spanners View Post
    Could you run two KVP valves parrallel to each other?
    OR
    Run the individual suction lines back to the engine room?

  11. #11
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Sporlan ORIT 15/20 installation tips

    Hello again everybody
    I'm sorry for the lack of information in my post, I'll try to give you some more details on the problem I'm trying to solve:
    wanted evaporation temperature 0-2°C , suction pression/temperature on compressor -17°C
    coil type A cooling capacity 42Kw, suction line leaving evaporator 42mm CU
    coil type B cooling capacity 16Kw, suction line leaving evaporator 35mm CU
    coil type C cooling capacity 11Kw, suction line leaving evaporator 28mm CU
    Again thank you everybody for your help and I apologize for the lack of info in my previous posts

  12. #12
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Sporlan ORIT 15/20 installation tips

    This is a long shot but i was playing with the idea of using EXV with controller such as Dixell XEV.

    You can control the amount of refrigerant in each coil via the EXV or an SV on the liquid line and/or the suction line.
    Any thoughts?

  13. #13
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Sporlan ORIT 15/20 installation tips

    So all three evaporators are to be running under similar conditions, at around 0-2*C?

  14. #14
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Sporlan ORIT 15/20 installation tips

    Yes Viking but they are located in different and far from each other location on the ship and have separate pipe lines going down to the engine room...
    I'll look in to your suggestion....
    Thank you though... :-)

  15. #15
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Sporlan ORIT 15/20 installation tips

    Quote Originally Posted by evapcoil View Post
    have separate pipe lines going down to the engine room...
    Quote Originally Posted by The Viking View Post
    OR
    Run the individual suction lines back to the engine room?
    Now, there is a thought...

    Why then can't the ORIT valves be located in the engine room???

  16. #16
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Sporlan ORIT 15/20 installation tips

    I think I found the solution: ORIT-PI-2/-3/-4
    This should work... :-)
    I can't put them in the engine because the pipes from these equipments join some other lines few decks above the engine room... It's quite a complicated and interconnected plant...

  17. #17
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Sporlan ORIT 15/20 installation tips

    Do we assume that you are getting your info from the Sporlan Literature website ?

    Such as this... http://www.sporlanonline.com/90-20-2.pdf

    From here... http://www.sporlanonline.com/literature.shtml
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  18. #18
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Sporlan ORIT 15/20 installation tips

    Yes Brian, I was reviewing that document, why? is it not reliable?

  19. #19
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Sporlan ORIT 15/20 installation tips

    Quote Originally Posted by The Viking View Post
    Evapcoil,

    It's somewhat hard for us to come with suggestions when we haven't been given any of the design parameters apart from that the valves has to be installed far from the hot gas pipe...

    The best anybody can do under these circumstances is to point you towards the manufacturers information so that you who have the design criteria can make the selection.
    Quote Originally Posted by evapcoil View Post
    Hello again everybody
    I'm sorry for the lack of information in my post, I'll try to give you some more details on the problem I'm trying to solve:
    wanted evaporation temperature 0-2°C , suction pression/temperature on compressor -17°C
    coil type A cooling capacity 42Kw, suction line leaving evaporator 42mm CU
    coil type B cooling capacity 16Kw, suction line leaving evaporator 35mm CU
    coil type C cooling capacity 11Kw, suction line leaving evaporator 28mm CU
    Again thank you everybody for your help and I apologize for the lack of info in my previous posts
    Quote Originally Posted by evapcoil View Post
    I think I found the solution: ORIT-PI-2/-3/-4
    This should work... :-)
    I can't put them in the engine because the pipes from these equipments join some other lines few decks above the engine room... It's quite a complicated and interconnected plant...


  20. #20
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Sporlan ORIT 15/20 installation tips

    What had I done of so horrifying? I know I might had been short on details, and I apologize for it but it is not easy to try to explain a system where we have three separate systems (positive temperature, low temperature and cooling back up for technical spaces) working with 4 compressors that can work with all the three system through a connecting manifold...
    On ships We have different needs than a regular system on land where space is not an issue... Here everything is compressed.. Saying this I'm not intending to offend anybody but in the mean time I find the "" face a bit out of place...
    Attached Images Attached Images

  21. #21
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Sporlan ORIT 15/20 installation tips

    Quote Originally Posted by evapcoil View Post
    Yes Brian, I was reviewing that document, why? is it not reliable?
    No, not at all, I was just checking that we were reading the same documents.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  22. #22
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Sporlan ORIT 15/20 installation tips

    ...and she said "give it to me you big fridgie"

  23. #23
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Sporlan ORIT 15/20 installation tips

    Well, 750 valve, thank you very much fior your suggestion, it seems it can work with the example configuration 1-1 :-)
    Thank you very much for the new prospective!