    Question about ceiling cassettes



    Hi Guys,

    Im soon going to be working on ceiling cassettes, I would just like to know, the built in condensate pump in the cassette, how many metres can it push water without the need of a seperate condensate pump, vertically or horizontally, and what extra pumps do you recommend for long runs, also in terms of servicing, how do you access condensate pan to acid flush all hard water and also how to access filters for cleaning and coils

    many thanks



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Question about ceiling cassettes

    The lift from the internal pump varies between the brands and models, typically you are looking at between 300 & 600 mm but the exact height will be in the manual for your units.
    The important bit is that the (condensate) pipe as it exits the cassette goes straight up to it's highest level and then slopes down from there. Also important if you got several cassettes on a common drain pipe, make sure the common pipe is below each cassette's drain's high point (to prevent one cassette pumping in to another)
    If the maximum lift isn't enough or the pipe can't be routed straight up to it's highest point then another pump is needed, this can be almost any tanked condensate pump. Personally I would steer away from the smallest ones with just 1 litre tank and go for something with 4+ litres.

    Access for service...
    The filter will just fold down on the centre part of the facia, as to the rest it will vary.
    The best you can do is to read the manual for the particular units you are about to install.

    OR,
    Better still,
    Speak to the manufacturer/importer/supplier of the units about getting on one of their training courses. Here in UK most of them are more than happy to give unit/brand specific training.


  3. #3
    Join Date
    Oct 2011
    Location
    united kingdom
    Posts
    17
    Rep Power
    0

    Re: Question about ceiling cassettes

    Thanks for your advice Viking,

    So say the run from the cassette to outdoor when you want the condensate to exit is say 3metres away, from the cassette, could you not just take hard plastic condensate in a straight line away to the outdoors or would it not push in a horizontal line that far? as you said you take the pipe up about 300mm then let it drop, what sort of distance in a horizontal straight would it push the water?

    Thanks

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    generally 1 cm drop over a meter for 1 cassette with 3/4 drain line check the cassette install manual for maximum pump lift-daikins/mitsi over 550mm-straight up,immediatly then run your fall and support it every metre or it will sag if it holds water
    Quote Originally Posted by asmaircon View Post
    Thanks for your advice Viking,

    So say the run from the cassette to outdoor when you want the condensate to exit is say 3metres away, from the cassette, could you not just take hard plastic condensate in a straight line away to the outdoors or would it not push in a horizontal line that far? as you said you take the pipe up about 300mm then let it drop, what sort of distance in a horizontal straight would it push the water?

    Thanks

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Question about ceiling cassettes

    I get some 3mm wire rope grips (look like tiny exhaust clamps) and use them to hold the 3/4 plastic pipe clips to the ceiling wires, theres a wire every two tiles so you can use these to get to the outside wall easily, and just loosen the rope grips to slide the drain up and down to get the fall correct.
    Mostly found in Oxfordshire, UK :)

  6. #6
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Question about ceiling cassettes

    The pump's in the units are not designed for horizontal discharge hence the term "lift pump".
    So even if your run is only three meters you should still utilise the lift available from the internal pump,you don't have to max it out but the greater the gravity fall you generate from the unit the less likely you are to have issues,Remember the pump in the unit is free may as well use it.
    Cheers
    Stu



    Quote Originally Posted by asmaircon View Post
    Thanks for your advice Viking,

    So say the run from the cassette to outdoor when you want the condensate to exit is say 3metres away, from the cassette, could you not just take hard plastic condensate in a straight line away to the outdoors or would it not push in a horizontal line that far? as you said you take the pipe up about 300mm then let it drop, what sort of distance in a horizontal straight would it push the water?

    Thanks
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    hello post #4- over 550mm-straight up,immediatly then run your fall - i quote haha

  8. #8
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Question about ceiling cassettes

    HAHA touchy little monkey today are we .How's your hamster/gerbil ??
    Cheers
    Stu
    Quote Originally Posted by install monkey View Post
    hello post #4- over 550mm-straight up,immediatly then run your fall - i quote haha
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    the beast is still currently under house arrest- gonna go wholesalers and get a 75mmsq 5 core swa to keep it occupied-if it was to bite me-its bye bye finger-you know what i mean haha

  10. #10
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Question about ceiling cassettes

    Get a T-REX rat trap and put some speaker cable in it to entice the little fooker .
    SNAP and he's history.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    personally id take it bungee jumping over a motorway bridge-but apparently its the family pet-and if i ever loose me snips then it could be of use-the boss is giving it another chance before we curry it!! i will keep u updated-if you want you can sponser it-just £30 a week as its rarer than a snow leopard!haha

  12. #12
    Join Date
    Jun 2010
    Location
    geraldton western australia
    Age
    39
    Posts
    57
    Rep Power
    14

    Re: Question about ceiling cassettes

    Quote Originally Posted by The Viking View Post
    The lift from the internal pump varies between the brands and models, typically you are looking at between 300 & 600 mm but the exact height will be in the manual for your units.
    except for LG. installed another one on friday (10kw) and checked the manual again (last did one 3 weeks ago and checked the manual in that too, nothing there either) but it still showed no mention of a max height for the drain.

    i just keep them under 500mm above the ceiling and have no problems.

  13. #13
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Question about ceiling cassettes

    ffs I can't believe someone hasn't already said this

    generally 1 cm drop over a meter for 1 cassette with 3/4 drain line check the cassette install manual for maximum pump lift-daikins/mitsi over 550mm-straight up,immediatly then run your fall and support it every metre or it will sag if it holds water

    as I am first to post the right answer I expect loads of rep for this!

  14. #14
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    rb post 4
    07-01-2012 05:56 PM#4install monkey

    VIP Poster I am starting to push the Mods: of RE


    Join Date Oct 2007Location manchesterAge 38Posts 1,624Rep Power7

    Re: Question about ceiling cassettes

    generally 1 cm drop over a meter for 1 cassette with 3/4 drain line check the cassette install manual for maximum pump lift-daikins/mitsi over 550mm-straight up,immediatly then run your fall and support it every metre or it will sag if it holds water

  15. #15
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Question about ceiling cassettes

    hi all i have installed ac cassettes before and tend to always use the lift if needing to get gravity for a distance. i have never knew that you can not run it out horizontally. until reading this post i have installed lots like where ran out horizontally. oops. having said that never had one call back or known of a issue because of this. in future will go up with them though.

    cheers

  16. #16
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    as a wise man told me- rtfm!! haha
    Quote Originally Posted by moondawn View Post
    hi all i have installed ac cassettes before and tend to always use the lift if needing to get gravity for a distance. i have never knew that you can not run it out horizontally. until reading this post i have installed lots like where ran out horizontally. oops. having said that never had one call back or known of a issue because of this. in future will go up with them though.

    cheers

  17. #17
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Question about ceiling cassettes

    haha busted!!!

  18. #18
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes


  19. #19
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Question about ceiling cassettes

    HAHA Monkey has taken to blowing smoke up his own arse.
    MY HERO !!!
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  20. #20
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    i only blow smoke out me arse- sorry!
    Quote Originally Posted by stufus View Post
    HAHA Monkey has taken to blowing smoke up his own arse.
    MY HERO !!!
    Cheers
    Stu

  21. #21
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Question about ceiling cassettes

    Quote Originally Posted by install monkey View Post
    cant get the link to work install got your other sanyo one which used rapidshare?

  22. #22
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Question about ceiling cassettes

    Quote Originally Posted by r.bartlett View Post
    ffs I can't believe someone hasn't already said this

    generally 1 cm drop over a meter for 1 cassette with 3/4 drain line check the cassette install manual for maximum pump lift-daikins/mitsi over 550mm-straight up,immediatly then run your fall and support it every metre or it will sag if it holds water

    as I am first to post the right answer I expect loads of rep for this!
    Nope, you're wrong, someone has already said that, no rep today.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  23. #23
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Question about ceiling cassettes

    Quote Originally Posted by Brian_UK View Post
    Nope, you're wrong, someone has already said that, no rep today.
    Which goes to prove no one actually reads other peoples posts before they jump in with their expert opinion.

    I cut and pasted IM's reply from post no/4 and even he didn't notice and even cut and pasted it back to me!!!!!!!!!!!!!!!!!!!!!!!!!!!!

  24. #24
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    sorry rb- i thought that was your response-as i didnt ask for brownie points-and as usual i didnt get any!-i do read all posts but sometimes i jump in with both feet with my input!

    Quote Originally Posted by r.bartlett View Post
    Which goes to prove no one actually reads other peoples posts before they jump in with their expert opinion.

    I cut and pasted IM's reply from post no/4 and even he didn't notice and even cut and pasted it back to me!!!!!!!!!!!!!!!!!!!!!!!!!!!!

  25. #25
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Question about ceiling cassettes

    Quote Originally Posted by install monkey View Post
    sorry rb- i thought that was your response-as i didnt ask for brownie points-and as usual i didnt get any!-i do read all posts but sometimes i jump in with both feet with my input!
    Just joshing with you of course but it does prove the point no one actually bothers to read threads properly so it ends up as posters repeating the same answer again and again as if it's new and enlightening

    Rep added btw ;-)
    Last edited by r.bartlett; 08-01-2012 at 05:05 PM.

  26. #26
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Question about ceiling cassettes

    install monkey figure 6.1 in that installation manual. am i missing something here but is it saying they can come out horizontal certainly looks that way?

  27. #27
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    horizontal only ifa 1cm drop over 1mtr , if you go up first it states within 150mm- if you enlarge the pic you will notice the fall


    Quote Originally Posted by moondawn View Post
    install monkey figure 6.1 in that installation manual. am i missing something here but is it saying they can come out horizontal certainly looks that way?

  28. #28
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    https://rapidshare.com/files/1121286...all_manual.pdf;
    daikin cassette manual- page 2 rise within 300mm and 675mm maximum lift

  29. #29
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Question about ceiling cassettes

    can sleep easier now install monkey thanks :-)

  30. #30
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    10yr ago i fitted a daikin 600sq cassette in my old bosses extension- 5kw he drylined his ceiling around the unit-didnt have much space as it was a pitched roof, due to the he knows best on how to run pipework- i had to fit a little giant 2ltr tank pump on top of the cassette, as the 3/8 braided hose terminates outside at low level,he has been exposed to the syphon effect-gurgling when the pump stops- thats if his pump hasnt died from being exposed to elephant snot syndrome- i sleep like a log haha

  31. #31
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Question about ceiling cassettes

    is that why he is your old boss now. interested if its still gurgling me. update required!!

  32. #32
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Question about ceiling cassettes

    the 50w spotlights have probably boiled off any condensate! he didnt fit an inspection hatch haha

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •