    Re: High and low pressure switch in air-cond

    Quote Originally Posted by Brian_UK View Post
    No.

    When the thermostat switches the circuit ON via terminal C the timer starts running for 5 minutes. After 5 minutes the compressor will be switched ON. The compressor will continue to run until the thermostat switches OFF.
    Then the short cycle timer locks out the control circuit should there be any attempt by the thermostat to start the compressor again within 5 minutes. After 5 minutes, timer then closes the control circuit and compressor is free to start when required, so long as pressure switches are also closed.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  2. #2
    Join Date
    Jan 2012
    Location
    malaysia
    Posts
    12
    Rep Power
    0

    Re: High and low pressure switch in air-cond

    How do i block the attempt by the thermostat to start the compressor again, cause in the diagram if the thermostat is off and on back it will attempt start the compressor within 5 minute.


    Quote Originally Posted by mikeref View Post
    Then the short cycle timer locks out the control circuit should there be any attempt by the thermostat to start the compressor again within 5 minutes. After 5 minutes, timer then closes the control circuit and compressor is free to start when required, so long as pressure switches are also closed.