    City Multi Poor Heating



    Just Started Up a new system earlier. Weighed in extra gas on cooling test mode. Reset system and ran on heating. All units ran but with poor off coil temp.System has 1 bc controller and 4 indoors. 2 Ducted and 2 wall. Checked all address all ok. System was pressured tested and held. Re checked extra charge and all ok. Anone with similar problem or any ideas



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: City Multi Poor Heating

    have u set the ports on the indoors to the bc box

  3. #3
    Join Date
    Jul 2010
    Location
    Ireland
    Age
    43
    Posts
    7
    Rep Power
    0

    Re: City Multi Poor Heating

    All indoors set to ports. Starts on heating standby and comes off all indoors run poor coil temp and poor compressor discharge temp.

  4. #4
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: City Multi Poor Heating

    Model numbers????
    Outdoor ambient temp?
    What were the indoor air on temps.
    How long had the power and control network been powered up for WITHOUT ANY interuption.
    Poor discharge temp. ......High or low???.
    Fill in the blanks and we'll see whats what.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  5. #5
    Join Date
    Jan 2012
    Location
    ENGLAND
    Age
    49
    Posts
    6
    Rep Power
    0

    Re: City Multi Poor Heating

    Are you happy with gas calc?
    What temp is discharge? Have you tried running only half the indoors in heating?
    It could be the system is over diversity and struggling in full heat over 100%.