    mitsubishi city multi



    Hi have 1501 fault on PURY-P250 gas charge is ok,so is operation pressures in heating and cooling but th 10 compressor shell temperature is 87 degrees c.could it be lack of oil in compressor.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: mitsubishi city multi

    how much oil did you lose when it leaked

  3. #3
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: mitsubishi city multi

    PURY-P250 YHM-A
    R410A/MEL32 3.5 Liters
    (Comp 2.0+ Line 1.5)

    I have no idea how much you lose.
    Hope this help

  4. #4
    Join Date
    Jan 2012
    Location
    ireland
    Age
    41
    Posts
    15
    Rep Power
    0

    Re: mitsubishi city multi

    Thanks don't know how much oil was lost due to leak as i have only taken over site.will add 1 litre a see from there.

  5. #5
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: mitsubishi city multi

    87c is only critical if running below 60hz for an hour
    Your unit is not loading up !
    Was the power dropped to the outdoor ,if so it won't run above 70hz for an hour after the power is restored.
    The oil separator in those units is very efficient.
    Oil is not your problem lack of compressor subcooling is.
    Do an LEV reset on the indoors
    Clean all the indoor filters and run it in test cooling
    Check the charge composition .Guessing R407c
    You're either short of gas or you've got a faulty LEV in an indoor or LEV1 in the outdoor ,or the comp is on the way out.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  6. #6
    Join Date
    Jan 2012
    Location
    ENGLAND
    Age
    49
    Posts
    6
    Rep Power
    0

    Re: mitsubishi city multi

    Do you have a comms room on the system? Could be lack of vapour back to the compressor due to low indoor unit index running. This can happen when there is only one indoor with demand on 24/7 on the system.
    Always worth checking out with this fault.

  7. #7
    Join Date
    Jan 2012
    Location
    ireland
    Age
    41
    Posts
    15
    Rep Power
    0

    Re: mitsubishi city multi

    Thanks found that alarm was being caused by faulty lev,was happening when only this unit was calling for cooling.

  8. #8
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: mitsubishi city multi

    Glad to hear it.
    Everyone likes a happy ending
    Cheers
    Stu