Re: High and low pressure switch in air-cond
Originally Posted by
huntersouls
Ok as you have explain, i dont quite understand how the compressor start running cause what i have see on the diagram it look like the timer is controlling the compressor to start and to off. For example i set my timer 5 minute and let the compressor run , does it mean that it will run 5 minute and then off it 5minute and then run back in 5minute?
No.
When the thermostat switches the circuit ON via terminal Y the timer starts running for 5 minutes. After 5 minutes the compressor will be switched ON. The compressor will continue to run until the thermostat switches OFF.
Last edited by Brian_UK; 08-01-2012 at 10:46 PM.
Reason: Wrong terminal number used.
Brian - Newton Abbot, Devon, UK
Retired March 2015