Results 1 to 25 of 25

Hybrid View

  1. #1
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: High and low pressure switch in air-cond

    Looks like R S T go to the phases and A B C are for the control circuit to turn the compressor contactor off in the event of a fault with the supply.
    Not sure if A B C are live in and out and a alarm contact or live in and out and a neutral like the kirwan phase protectors as your diagram is not clear.
    Just trace the wires on the diagram and see where they go. Or phone the manufacturers tech dept.
    Mostly found in Oxfordshire, UK :)

  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: High and low pressure switch in air-cond

    its a common ,no,nc contact-stick 415v on and test continuity on a to b or c to work out ur control circuit,also disconnect the 415v to prove the contact breaks also-carefully and safely

  3. #3
    Join Date
    Jan 2012
    Location
    malaysia
    Posts
    12
    Rep Power
    0

    Re: High and low pressure switch in air-cond

    Does it mean i need give external power to it on the common pin?


    Quote Originally Posted by install monkey View Post
    its a common ,no,nc contact-stick 415v on and test continuity on a to b or c to work out ur control circuit,also disconnect the 415v to prove the contact breaks also-carefully and safely

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: High and low pressure switch in air-cond

    your low voltage control circuit will loop through the normally closed contact(when 415v is present to the relay
    Quote Originally Posted by huntersouls View Post
    Does it mean i need give external power to it on the common pin?