09-01-2012, 10:56 PM #1
Re: High and low pressure switch in air-cond
Looks like R S T go to the phases and A B C are for the control circuit to turn the compressor contactor off in the event of a fault with the supply.
Not sure if A B C are live in and out and a alarm contact or live in and out and a neutral like the kirwan phase protectors as your diagram is not clear.
Just trace the wires on the diagram and see where they go. Or phone the manufacturers tech dept.Mostly found in Oxfordshire, UK :)
-
09-01-2012, 11:02 PM #2
Re: High and low pressure switch in air-cond
its a common ,no,nc contact-stick 415v on and test continuity on a to b or c to work out ur control circuit,also disconnect the 415v to prove the contact breaks also-carefully and safely
-