    Reciever PRV vent pipe???



    Whats the propper practice with these things, i assume they need piping outside of the plant room but is there any guidlines on where to and to what height and does it need a thingy on the end to stop it getting bugs water or stuff in it and blocking it up?

    Did see a mushroom shaped brass thing for boiler vent pipes and wonder if something like this would be an idea...

    or a whistle off a steam engine

    Jon


    Mostly found in Oxfordshire, UK :)

  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Reciever PRV vent pipe???

    boiler vent pipes are supposed to vent to a visible area,safely and discharge either against the wall or at low level as you have think if a relief valve discharges hot water at 3.5bar or gas at 28 bar then if you harm anyone then your up in court,do not pass go,or collect £200!!

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Reciever PRV vent pipe???

    Discharge is required to be at least 4.5mtrs above ground level and 6mtr from windows,doors or vents.The discharge should be terminated in a manner which prevents discharged refrigerant being sprayed directly at individuals nearby and prevents debris from entering and clogging the discharge port . A specially designed diffuser is recommended,such as a whisper-flow vent diffuser.
    http://www.documentation.emersonproc...102747x012.pdf
    SOURCE=unknown APC maybe.
    Cheers
    Stu
    Last edited by stufus; 05-01-2012 at 07:03 PM. Reason: forgot a bit
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Reciever PRV vent pipe???

    Pretty sure it has to be in steel pipe work too

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Reciever PRV vent pipe???

    Just to be clear, this is a relief valve on a liquid reciever and not a boiler as i may have given the impression it was