    Help !! NRV requirement in a KTK chiller.



    Hi all, this is my first post so be kind (and helpfull please).

    We have some KTK chillers and are being told by the supplier that there needs to be a modification to fit non return valves in the compressor discharge lines before the common header. They are saying this will solve reliability issues and is a production mistake.

    Does this make sense and will it help reliability? Your thoughts please.

    Ta, Mark.



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Help !! NRV requirement in a KTK chiller.

    Make's perfect sense .
    The lack of NRV's on the compressor discharge means even if a compressor is not running it will still be subject to full discharge pressure generated by the other compressors.
    This can cause a lot of expensive problems on start up!!!
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Help !! NRV requirement in a KTK chiller.

    even more expense if theyre fitted the wrong way!!!
    Quote Originally Posted by stufus View Post
    Make's perfect sense .
    The lack of NRV's on the compressor discharge means even if a compressor is not running it will still be subject to full discharge pressure generated by the other compressors.
    This can cause a lot of expensive problems on start up!!!
    Cheers
    Stu

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Help !! NRV requirement in a KTK chiller.

    Also, if it is recommended by the manufacturers then it would make sense to have the modification carried out.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Help !! NRV requirement in a KTK chiller.

    Hi Mark and welcome to the forum.
    Yours is not a new dilemma.
    Stufus and Brian make good points! (As usual)

    The need for a non return valve seems to have become more necessary as the use of smaller multiple compressors has become more prevalent.
    Basically earlier versions of scroll type compressors had weak internal non return / discharge valves.
    Which would struggle to cope with the amounts of condensed vapour / liquid.
    That could collect in the discharge pipe between the condenser and compressor.
    Resulting in effectively a "Head of Liquid" sitting on top of the compressors upon start-up.
    With the modern highly compact chiller (Not sure of your particular design?)
    The need for a non return valve is even more relevant, particularly with the newer Condensers using "free cooling " options.
    Add the fact that many chillers have condenser coils that are designed for use in more countries (read hotter climates).
    You have larger than necessary condensers acting in some instances like receivers, were is the condensed liquid going to sit?

    Long winded I know but hopefully you get the gist of what I mean?
    Cheers Grizzly

  6. #6
    Join Date
    Apr 2011
    Location
    India
    Age
    36
    Posts
    94
    Rep Power
    14

    Re: Help !! NRV requirement in a KTK chiller.

    Hi,

    NRVs are used not in multiple compressor chillers but also in the single compressor chillers.York single compressor chillers have NRVs at their discharge.

    As Grizzly mentioned, " free cooling " options.What does it mean, I have never heard about this term.Can anyone please explain it ??

    Cheers

    Sumit.

  7. #7
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Help !! NRV requirement in a KTK chiller.

    READ THIS
    http://en.wikipedia.org/wiki/Free_cooling

    Cheers
    Stu

    Quote Originally Posted by Sumit View Post
    Hi,

    NRVs are used not in multiple compressor chillers but also in the single compressor chillers.York single compressor chillers have NRVs at their discharge.

    As Grizzly mentioned, " free cooling " options.What does it mean, I have never heard about this term.Can anyone please explain it ??

    Cheers

    Sumit.
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  8. #8
    Join Date
    Apr 2011
    Location
    India
    Age
    36
    Posts
    94
    Rep Power
    14

    Re: Help !! NRV requirement in a KTK chiller.

    Hi Stufus ,

    Its very well explained there.But can you please briefly explain the method " Refrigeration Migration " of free cooling.I have some confusion regarding this, not able to understand it completely.


    Cheers

    Sumit

  9. #9
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Help !! NRV requirement in a KTK chiller.

    Refrigerant will always move (migrate) to the coldest part of the system ,it eliminates the need for compressor operation as the fans and heat diff with the water in the hydraulic circuit and cooling tower provide the heat gain and rejection the maintain changes in state(vapour to liquid and liquid to vapour) effectively providing free cooling.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Help !! NRV requirement in a KTK chiller.

    Quote Originally Posted by Grizzly View Post
    You have larger than necessary condensers acting in some instances like receivers, were is the condensed liquid going to sit?
    Cheers Grizzly
    The bottom third of the condenser is designed for the liquid.
    If liquid returns to the compressor head from the top of the condenser, you are way over charged.

    In general, when there is more then 1 compressor or the condenser above the compressor, a NRV should be installed.
    Do not forget a crankcase heater. protecting the compressor from liquid.