Results 1 to 10 of 10
    Jan 2012
    United kingdom
    1
    Help !! NRV requirement in a KTK chiller.
    Hi all, this is my first post so be kind (and helpfull please).
    We have some KTK chillers and are being told by the supplier that there needs to be a modification to fit non return valves in the compressor discharge lines before the common header. They are saying this will solve reliability issues and is a production mistake.
    Does this make sense and will it help reliability? Your thoughts please.
    Ta, Mark.
    Jun 2009
    Lusk , Dublin
    1,115
    Re: Help !! NRV requirement in a KTK chiller.
    Make's perfect sense .
    The lack of NRV's on the compressor discharge means even if a compressor is not running it will still be subject to full discharge pressure generated by the other compressors.
    This can cause a lot of expensive problems on start up!!!
    Stu
    Tool's ? check ! Condom's ? check !
    Oct 2007
    manchester
    5,639
    45
    even more expense if theyre fitted the wrong way!!!
    Quote Originally Posted by stufus View Post
    Stu
    11,025
    Also, if it is recommended by the manufacturers then it would make sense to have the modification carried out.
    Somerset
    69
    4,697
    Hi Mark and welcome to the forum.
    Yours is not a new dilemma.
    Stufus and Brian make good points! (As usual)
    The need for a non return valve seems to have become more necessary as the use of smaller multiple compressors has become more prevalent.
    Basically earlier versions of scroll type compressors had weak internal non return / discharge valves.
    Which would struggle to cope with the amounts of condensed vapour / liquid.
    That could collect in the discharge pipe between the condenser and compressor.
    Resulting in effectively a "Head of Liquid" sitting on top of the compressors upon start-up.
    With the modern highly compact chiller (Not sure of your particular design?)
    The need for a non return valve is even more relevant, particularly with the newer Condensers using "free cooling " options.
    Add the fact that many chillers have condenser coils that are designed for use in more countries (read hotter climates).
    You have larger than necessary condensers acting in some instances like receivers, were is the condensed liquid going to sit?
    Long winded I know but hopefully you get the gist of what I mean?
    Cheers Grizzly
    Apr 2011
    India
    36
    94
    14
    NRVs are used not in multiple compressor chillers but also in the single compressor chillers.York single compressor chillers have NRVs at their discharge.
    As Grizzly mentioned, " free cooling " options.What does it mean, I have never heard about this term.Can anyone please explain it ??
    Sumit.
    Jun 2009
    Lusk , Dublin
    1,115
    READ THIS
    http://en.wikipedia.org/wiki/Free_cooling
    Stu
    Quote Originally Posted by Sumit View Post
    Sumit.
    Apr 2011
    India
    36
    94
    14
    Hi Stufus ,
    Its very well explained there.But can you please briefly explain the method " Refrigeration Migration " of free cooling.I have some confusion regarding this, not able to understand it completely.
    Sumit
    Jun 2009
    Lusk , Dublin
    1,115
    Refrigerant will always move (migrate) to the coldest part of the system ,it eliminates the need for compressor operation as the fans and heat diff with the water in the hydraulic circuit and cooling tower provide the heat gain and rejection the maintain changes in state(vapour to liquid and liquid to vapour) effectively providing free cooling.
    Stu
    Sep 2003
    ISRAEL
    72
    4,248
    Cheers Grizzly
    The bottom third of the condenser is designed for the liquid.
    If liquid returns to the compressor head from the top of the condenser, you are way over charged.
    In general, when there is more then 1 compressor or the condenser above the compressor, a NRV should be installed.
    Do not forget a crankcase heater. protecting the compressor from liquid.