Thread: RTAD Oil sensor
04-01-2012, 07:12 PM #1
RTAD Oil sensor
Does anyone have a part number for Oil Return temp sensor 3R30-2 for an RTAD 145.
I have SEN numbers and cant determine which it is ie. SENS00132 or 00202, 00296, 00306 or 00951. My guess is the 00132 (32-121* 0.250 Dia.LG 4")
Any help appreciated
04-01-2012, 10:05 PM #2
Re: RTAD Oil sensor
Hi centrifs.
I cannot find the part number for you!
But perhaps the attached will help for future referance?
Attachment 8549
05-01-2012, 06:08 AM #3
Re: RTAD Oil sensor
The sensor is SEN00132. You may also need a CON00204 if sensor is not in a well but immersed
Regards,
CV
05-01-2012, 08:31 AM #4
Re: RTAD Oil sensor
Thanks CV Geardrive. have you seen these leak at the end of the cable in electrical comparment.??
05-01-2012, 10:13 AM #5
Re: RTAD Oil sensor
Hi Centrifs,
Usually this problem occurs in EVP saturated and suction sensors.
If you have this kind of problem in oil sensor means that the con00204 is too tight and crack the body of sensor.
Con00204 can be used once. After you tight it to sensor you cannot remove all parts of con from sensor.
Regards,