    Frozen filter drier



    Need some urgent help, Please.

    Temperature in our cold storage suddenly becomes warm. Compressor is running but I noticed that there are ice building up on the filter drier and the TXV. Is it an indication of clogged filter, co'z the unit was running perfectly before. Also I noticed that the compressor has very little oil. What is the suitable oil for my compressor. It was from Carrier and the refrigerant is 134A.

    Thanks!!!



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Frozen filter drier

    You are right, drier is blocked, refrigerant flows slower, oil doe's not return.
    Replace the drier and see how the temp drop.

  3. #3
    Join Date
    Dec 2011
    Location
    Spain
    Age
    39
    Posts
    22
    Rep Power
    0

    Re: Frozen filter drier

    If you have enough oil to run the compressor, don't fill with new oil the installation. It will go back to the oil separator / compressor once you have changed the filter and started again the installation.

  4. #4
    Join Date
    Jan 2012
    Location
    Philippines
    Age
    48
    Posts
    6
    Rep Power
    0

    Re: Frozen filter drier

    Thank you, Just waiting for the new filter.