Results 1 to 35 of 35
    May 2011
    Malaysia
    28
    Unhappy Water Drips/ Water Splashing out on indoor wall mount evaporator, VRF VRV problem
    Hello there folks,
    I have only recently joined the force as a service engineer.
    Here in Malaysia it is quite hot and humid.
    We have this problem with vrv/vrf system installed in a hotel.
    When ac switched off, the indoor wall mount units feels cold when the evaporator is touched.
    because the indoor units are not switched on, hence the blower isnot working, and if left for a long time, the evaporator gets cold enough and starts dripping on the louver.
    out of the entire system, about 6~8 indoor wall mount units suffer bad leaks termed ac sweating.
    the rooms have bout 75% humidity, due to that it makes the dripping quite bad.
    We believe that the expansion valve at the indoor unit does not fully close and that is how
    refrigerant seeps to the evaporator.
    Solutions:
    1. Some say install a dehumidifier
    2. others recommend a heater and a thermostat control to deter condensation.
    which of this can help with the problem?
    *Bare in mind that if the indoor units are switched on always, we do not have a condensation problem on the evaporator, however this is a hotel and when guest checkout these units are
    in individual rooms are left switched off long enough and start dripping.
    do advice me folks...
    Im trying to seek a cost effective/simple way to solve the prob, but unsure if dehumidifier etc would do the job.
    Oct 2007
    manchester
    5,639
    45
    Re: Water Drips/ Water Splashing out on indoor wall mount evaporator, VRF VRV problem
    what make is your system-if mitsi then perform a reset and this will realign lev heads-also mitsi are problematic for lev heads detatching themselves from lev bodys
    May 2011
    Malaysia
    28
    mines Fujitsu VRF.
    When you say reset you mean reset power and restart the entire system ?
    I have done that. hoping the indoor valve would sit at proper original position when unit power off.
    however there might be some dirt stuck in the valve not allowing it to fully shut, as in very tiny gap so gas seeps through making the unit sweat after approx 6~10hrs power off!.
    what are lev heads ?
    *besides that if I can use a dehumidifier or somesort that would reduce humidity so help prevent the refrigerant from seeping into evaporator during unit power off would be great.
    Oct 2007
    manchester
    5,639
    45
    lev heads are the indoor valves you have been referring to, if you stop all indoor units does the condenser still run? sticking/welded contactor. can you run the system in full heating to maybe flush the system?
    May 2011
    Malaysia
    28
    If i stop all indoor units , the outdoor(condenser) does not run.
    I have not tried heating to flush the system, perhaps that one solution and then monitor it.
    I do not think there is a problem with the contactors.
    we have an Inverter compressor and one constant compressor in each outdoor unit.
    thanks for the replies mate...
    helpful discussion...
    Feb 2007
    2,473
    45
    Hmmm,
    How old is this system?
    Was it properly commissioned?
    My first check would be to:
    Turn all indoor units OFF, then start just one of the indoor unit you got problem with. Start it in cooling, set at minimum temperature.
    Leave the other indoor units turned off on their remotes, or the central controller, whatever you got.
    -Does the running unit perform well?
    If not you got an installation problem, where the system "speaks" to the wrong indoor unit.
    Only after the system passed this test would I start taking things apart and that's when things gets complicated...
    You mentioned that you were new to this game? Any chance that you could get a more experienced engineer in to help you with this?
    VRV/VRFs are complicated and not easy to learn trouble shooting on...
    Sorry
    Oct 2007
    manchester
    5,639
    45
    morning viking-good to see your alive and kicking
    jumper's Avatar
    jumper Guest
    Fan should keep going long enough to warm & dry evaporator.
    Feb 2007
    2,473
    45
    Quote Originally Posted by install monkey View Post
    Thank you, just starting to wake up from my hibernation...
    Sep 2003
    ISRAEL
    72
    4,248
    Quote Originally Posted by The Viking View Post
    Its about time, you got some people here seriously worried.
    Welcome back.
    Somerset
    69
    4,697
    Hmmm,
    Sorry
    Yes ditto.
    Welcome back my friend.
    May 2011
    Malaysia
    28
    system is approx 1 year old now or slightly short of a year.
    we are only going to resume troubleshooting very soon to diagnose d prob.
    the hotel is open to guest, they just try keep d rooms used, or atleast keep the indoor units wiped as n when it starts drippin (usually after more then 12hrs switched off).
    It was commisioned by other engineers, im only recently taking over.
    I hope to learn much and fast.
    *to answer your question, yes the system corresponds to the correct indoor unit,
    and it runs fine.
    i have tried that during my previous visit.
    thanks viking... you must be quite d veteran i presume ?
    hehe salute
    hoping to learn from u guys..
    cooling is now my job!
    Feb 2007
    2,473
    45
    Quote Originally Posted by rashVRF View Post
    Not a veteran I'm afraid, just old.
    As you are looking at more than one indoor unit with the same fault, EEVs not closing, on a newish system, then there aren't many things that could cause it.
    Something is stopping all those valves from shutting. If there were one valve after a year, yes, it could be a manufacturing fault on the valve but you are talking 6 to 8 valves here. Extremely unlikely that they all failed of their own.
    My best guess, remember that I'm a couple of thousand miles away, is that this system has "grit" in it.
    Most likely whoever installed it did so without using OFN when they did brazings.
    Only way to tell is to cut a strainer out to have a look.
    Quick fix- don't turn indoor units OFF, leave them ON, in fan only if needed.
    But, this is likely to cause compressor failures.
    Better fix(and expensive)- cut driers in to the suction lines just before each compressor and change these frequently until you got a clean system.
    Best fix- using a flushing agent to flush the system and then replace the oil.
    But this is complicated and timeconsuming/expensive.
    Good luck, and don't forget the most important bit...
    Let us know what you find.
    Apr 2009
    israel
    778
    if all else mentioned above fails,resort to setting all units that are stopped for a few hours,to come on and operate for a few minutes ,this however is a awkward solution .
    lev's should not have a leak that big, to allow liquid rerigerant to accumalate and cause what you discribe.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
    May 2010
    japan
    Pleasechargetoapproximately5%gas
    Jun 2009
    Lusk , Dublin
    1,115
    Is the power to the indoor unit's being dropped via a card reader or something similar.
    If so this could be the cause of your problem ,resulting in the LEV heads ending up put of sync with the control's
    The control's will think the valve is closed when in fact it is 12/20/30% open causing evap to flood when unit is off as the valve can't drive closed if the power is off !!
    When power is returned the unit will presume the valve is closed and the cycle will continue every time the power is dropped out so the problem gets progressively worse.
    But as suggested above lack of OFN purging during installation is also a very likely cause of your symptoms.
    Stu
    Tool's ? check ! Condom's ? check !
    Oct 2011
    new zealand
    22
    some good advice on this thread. i was guessing the wiring do not match the pipe work but you say its all good. so sounds like it could be a dodgy install. will fujitsu cover the unit if a dryer is installed on a r410a system? flush system and recharge with dryer if allowed might be your cheapest bet
    May 2011
    Malaysia
    28
    Quote Originally Posted by kanchi View Post
    What do you mean?
  19. #19
    May 2011
    Malaysia
    28
    Quote Originally Posted by stufus View Post
    Stu
    Hmm, i would also like to give this a check, maybe turn off d effected indoors using remote not by card reader, then monitor temp after LEV during switched off state ~ can do somesort of a comparison wit another unit by switchin off (removing card reader).
    Also likr what was previously mentioned, try heating to temp flush!
    I will b visitng site by early Feb and would want to try these methods to futher diagnose d system... Thanks again guys, i will keep d thread further updated wit my findings.
    Thanks for d suggestions.
  20. #20
    Jun 2009
    Lusk , Dublin
    1,115
    Turning off by the controller will not sort the problem until all the LEV's are reset as they will still be out of step and even with the controller they may not drive fully closed.
    Stu
  21. #21
    May 2010
    japan
    What do you mean?
    I'm sorry
    I waswrongin Englishtranslation.
    I think
    For a5%chargeVRV AC
    LEVbadcase ofVRV VRF
  22. #22
    Jun 2009
    Lusk , Dublin
    1,115
    Well that clears that up
    Stu
    I'm sorry
    I think
    For a5%chargeVRV AC
  23. #23
    Apr 2005
    INDIA
    63
    84
    dear rash
    It seems ur solenoid valve is faulty or might not be connected properly to the circuit that is the reason it is not shutting when unit is off, or system might be dirty inside.
    I had a similar problem it was with four indoor unit, it was faulty solenoid valve it used to start leaking every year. finally we put a shut of valve in series, whenever unit is not in use! put off the valve!
    regds.
  24. #24
    May 2011
    Malaysia
    28
    Stu
    Best i can do is to turn off power wait for 30 seconds and back on, and wait... Keep doin that with the main power until the valve heads sits at proper position. Perhaps if i do that 5 times it wud help the lev find the original start position, correct? Otherwise how else to reset its position?
  25. #25
    Apr 2009
    israel
    778
    couldnt put it in better words!!
    best regards
  26. #26
    Jun 2009
    Lusk , Dublin
    1,115
    I'm not to sure Rash ,most manufacturers have a procedure for resetting their valves ,I'm not familiar with the Fujitsu procedure .
    If the system has a reclaim mode which opens all valves for recovery you could try activate this and then cancel it which should drive all the valves closed.
    Stu
  27. #27
    Jan 2012
    Australia
    8
    I was going to say the same thing as Stufus.
    If the indoors are getting isolated by the card reader, then it can cause this (seen it before)
    Re-wire one to constant power and turn it off with the remote only, this should power down the valve and shut it completely. if that doesnt fix it, then id be putting money on scale in the system from pipe brazing.
  28. #28
    MR T's Avatar
    MR T Guest
    maybe gas not enought
  29. #29
    May 2011
    Malaysia
    28
    Quote Originally Posted by mr t View Post
    could lack of gas cause such an issue ?
  30. #30
    Apr 2007
    36
    371
    23
    Quote Originally Posted by MR T View Post
    Ahh the old "something isn't working blame the charge" ............
    I doubt it, i would make a bet that its the valves not closing off correctly
    J
  31. #31
    Apr 2012
    Uk
    44
    13
    I would say that stufus has hit the nail on the head with this issue, something is stopping the operation of these units before the expansion device has driven into its closed position.
  32. #32
    Apr 2012
    Uk
    44
    13
    Rash, do you have model no of outdoor and indoor units??
  33. #33
    Jun 2009
    Lusk , Dublin
    1,115
    It's not short of gas !!!
    Your LEV's are out of step..
    Ring Fujitsu for the vale reset procedure.
    Even oxidisation would not cause this amount of valve issues ,(unless the pipe work was full of water during installation)
    Stu
  34. #34
    Apr 2007
    36
    371
    23
    What do you mean its not short of gas! It's always the gas!!!
    J
    Stu
  35. #35
    Apr 2012
    Uk
    44
    13
    I'm pretty sure on the AOY type outdoor unit, sw2-3 (on) is the electronic expansion valve initialization... however can't believe a system of this age would have that many valves out of sink without some external interference.