    Compressor Label R134a but the label inside the unit is R404a



    I will repair a Desmon chiller I see the label inside the unit it is R404a refrigerant but when I see the compressor the label is R134a. That why I cannot start to repair because I dont know what refrigerant I will use. Can you help me with this. Thank You



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Compressor Label R134a but the label inside the unit is R404a

    has the compressor been changed before? what does the expansion valve say- probably best to contact the manufacturer for comfirmation

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Compressor Label R134a but the label inside the unit is R404a

    In your ambient, it would most likely to be R-134a, Difference between compressor for 134 and 404 is displacement.
    Check the running pressure, it might help you.

  4. #4
    Join Date
    Feb 2005
    Location
    United Kingdom
    Age
    73
    Posts
    18
    Rep Power
    0

    Re: Compressor Label R134a but the label inside the unit is R404a

    Check the system pressure after it has been standing off for some time,check your ambient temperature then use a comparator to get the pressure/temperature readings and you will then know what the system is charged with

  5. #5
    Join Date
    Apr 2010
    Location
    australia
    Age
    45
    Posts
    78
    Rep Power
    15

    Re: Compressor Label R134a but the label inside the unit is R404a

    check your t.x valve.