Results 1 to 25 of 25
  1. #1
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Hanging evaps in cold rooms



    Client has a long room which we are going to fit out with fridge kit. Consists of 2 x 2kw way blow evaps. The crunch is that we are not allowed to penetrate the ceiling of the room as it is to be outside and uncovered. We normally use the pvc mushroom coach bolts but he's refused.

    I really don't want to span the room with channel and supports from the side walls so considering it's a std 100mm injected foam coldroom panel what do you tricky types use instead



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Hanging evaps in cold rooms

    5.5x25tech screws with m6 penny washers through the unistrut will hold it!

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Hanging evaps in cold rooms

    Not to sure RB ,Can you pierce the inner layer?
    If so I'd use stainless self tappers and stainless Mupro base's
    How are you getting the pipework out of the room?
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  4. #4
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Hanging evaps in cold rooms

    all holes out the side wall only. inner skin can be pierced. I was thinking about the spring toggles

    what are mupro bases??
    Last edited by r.bartlett; 27-12-2011 at 11:07 PM.

  5. #5
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Hanging evaps in cold rooms

    Good to go so
    Just be sure to use stainless self tappers or tech's and you'll have no problem's
    Or that no more nails stuff is good I hear
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Hanging evaps in cold rooms

    Tek screws, or put wall mount evap, or tell customer to provide fixings!
    Mostly found in Oxfordshire, UK :)

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Hanging evaps in cold rooms

    If they are wedge coolers then self tappers no bother, if box coolers then you will need spring bolts or unistrut spanning the ceiling, other wise some sagging will occur.

    Allternatively use upright steel at the end of the room and use cantilever brackets to hang the cooler (1m brackets)

    al
    Mostly found in the southern part of this green and pleasant land.

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Hanging evaps in cold rooms

    Canta lever frames through the side walls, pipes as well. Not rocket science

  9. #9
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Hanging evaps in cold rooms

    If its new build get some wood moulded in the roof panel for coach screws.
    Mostly found in Oxfordshire, UK :)

  10. #10
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: Hanging evaps in cold rooms

    Last edited by cool runings; 28-12-2011 at 12:45 AM.

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Hanging evaps in cold rooms

    good for plasterboard but when they expand they need 20mm of substance to prevent them dropping out
    http://www.leofixings.com/fixings-pr...1-384-388.html
    Quote Originally Posted by cool runings View Post
    Last edited by install monkey; 28-12-2011 at 10:01 AM.

  12. #12
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Hanging evaps in cold rooms

    This is a Mupro base ,probably known as something else over yonder



    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Hanging evaps in cold rooms

    its a back plate up north

  14. #14
    Join Date
    Nov 2008
    Location
    birmingham
    Posts
    155
    Rep Power
    19

    Re: Hanging evaps in cold rooms

    maybe strut on the internal wall and bolt some upside down cantilever arms at the top of the strut to suspend the unit from, simples!

  15. #15
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Hanging evaps in cold rooms

    Quote Originally Posted by Kev The Tool View Post
    maybe strut on the internal wall and bolt some upside down cantilever arms at the top of the strut to suspend the unit from, simples!
    Job starts on 3rd Jan in Leicester so we will see how simples it is :-)

  16. #16
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Hanging evaps in cold rooms

    Hi RB.
    I cannot believe no-one has mention Nutserts also sometimes known as threaded rivet inserts.
    Absolutely brilliant for blind fixing especially into thin sheet materials.
    Using these you could fix whatever suspension channel or thread bars you want, wherever you want.

    Check out the link for a description of what I mean!

    Available from RS, Screwfix etc.
    http://www.albert-jagger.co.uk/Porta...1_nutserts.pdf

    Grizzly

  17. #17
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Hanging evaps in cold rooms

    grizzly thats coz were engineers and we make do with what we have in our vans-i had to hang 2 daikin 71 cassettes in a petrol station and that had only a corrugated clad roof- i had to use pozi screws on a cable tray stand off bracket to hang m8 rod- this was 20yr ago- for 2 yr i never walked underneath them!!!

  18. #18
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Hanging evaps in cold rooms

    That's why Grizzly's on the big bucks(and showing his age ,us kid's don't use rivets)
    If it doesn't involve power tool's it's old hat.
    Cheers
    Stu
    Last edited by stufus; 29-12-2011 at 12:20 PM. Reason: added a few smiley's to avoid the wrath of the bear
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  19. #19
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Hanging evaps in cold rooms

    Quote Originally Posted by install monkey View Post
    grizzly thats coz were engineers and we make do with what we have in our vans-i had to hang 2 daikin 71 cassettes in a petrol station and that had only a corrugated clad roof- i had to use pozi screws on a cable tray stand off bracket to hang m8 rod- this was 20yr ago- for 2 yr i never walked underneath them!!!
    Should have used mupro base's or back plates as they are known up norff.HAHA
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  20. #20
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Hanging evaps in cold rooms

    Quote Originally Posted by install monkey View Post
    grizzly thats coz were engineers and we make do with what we have in our vans-i had to hang 2 daikin 71 cassettes in a petrol station and that had only a corrugated clad roof- i had to use pozi screws on a cable tray stand off bracket to hang m8 rod- this was 20yr ago- for 2 yr i never walked underneath them!!!
    Remember being on a site where we were hanging some Mastair ceiling units. (not spec'ed by us of course) Told it was a solid concrete ceiling so drilled in and ah it's a hollow concrete ceiling. As it was a g.ment base getting on/off site was a nightmare Ended up hanging them on 6mm spring toggles instead. Never went back and never wanted too!

  21. #21
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Hanging evaps in cold rooms

    Nice to see the festive humour guys

    Or am I getting slow in my old age?

    I understand your dilemma IM all to well. (I am still on the tools my friend!)
    Although I am no longer known as a "Engineer" now I am a "Service Technician!"
    The only difference for me is I have a large shed full of "Options" from various previous jobs over the ages.
    So yes as budgets get squeezed ever tighter even my once plentiful stock is getting depleted.

    RB's is not a mickey mouse company and I suspect that his budget can stretch to a Nutsert kit and hand insertion tool.

    Stufus.
    I still have a large Yankee Screwdriver which I can still fall back on if the batteries fail!
    Big Bucks! That's debatable. A regular income is nice though.

    You will never earn a fortune as PAYE (pay as you earn) - re how we in the UK pay income tax. (For our non UK / Irish colleagues.) If you want that you have to be self employed.
    However being self employed has it's problems especially in a recession.

    But you know all that don't you my friend.


    Happy New Year to you all.
    Grizzly
    Last edited by Grizzly; 29-12-2011 at 02:19 PM.

  22. #22
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    78
    Posts
    195
    Rep Power
    17

    Re: Hanging evaps in cold rooms

    If you use fixings that only penetrate the inner skin won't this cause the roof panel to de-laminate and sag?

  23. #23
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Hanging evaps in cold rooms

    Quote Originally Posted by Frikkie View Post
    If you use fixings that only penetrate the inner skin won't this cause the roof panel to de-laminate and sag?
    He'll be long gone by the time that happens...
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  24. #24
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Hanging evaps in cold rooms

    a 2kw cooler is going to weigh approx 20kg! hardly going to bring the roof down

  25. #25
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Hanging evaps in cold rooms

    Quote Originally Posted by Frikkie View Post
    If you use fixings that only penetrate the inner skin won't this cause the roof panel to de-laminate and sag?
    NO Chance!
    Have you ever tried to de-laminate or remove the outer on a Cold store panel.
    If the panel sags its because the panel vapour seal has been compromised and is saturated with water.
    The chances of that happening from inside out is Zilch!
    As the guys have stated if a self tapper is adequate then Nutserts are Guaranteed.

    If in doubt spread the load with multiple fixings.

    Grizzly

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •