    Thumbs up TEV selection



    In order to select a proper TEV from the manufacturer catalouge, most of the times the required capacity can not be found. For example for 9kW cooling capacity, the nearest listed capacity is 7kW or 11 kW. Each one gives different nozzle size.Which one the best choice and why?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: TEV selection

    Hi Lana,

    Its because you can adjust the TXV.

    I would use the 11KW to get 9KW and just close it a bit.

    Chemi

  3. #3
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: TEV selection

    Mr. O'Brian,
    Can you explaine why 11kW? Is it possible to select the 9kW and then ajust the valve to get the required capacity?
    Thanks
    Even Einstein Asked Questions

  4. #4
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: TEV selection

    Industry convention selects the larger valve, the 11kW over the 7kW.
    While I don't strongly disagree, Marc, my experience is that a slightly undersized valve will hunt less than its oversized equivalent. In cases where you are wanting to maintain as low a superheat as possible, I would favor the undersized TEV.

  5. #5
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: TEV selection

    Would you please give me a quick hint what is the static superheat and what's the difference between static and total superheat?
    Cheers.
    Even Einstein Asked Questions

  6. #6
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: TEV selection

    Lana, I think Marc means "Spring pressure" when he refers to static superheat. Not sure about "total superheat" but I would hazard a guess that we bring the equalizing and powerhead pressures into the picture... these, of course, are dynamic, as opposed to static, and complete the picture of an expansion valve's behavior.

  7. #7
    Ian Ship's Avatar
    Ian Ship Guest

    Smile Re: TEV selection

    Always undersize the expansion valve. Oversized valves will hunt.

    Then adjust the superheat to give 5 to 6 degrees
    Last edited by Ian Ship; 04-12-2007 at 12:20 AM.

  8. #8
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: TEV selection

    Hi Lana,

    I agree with Dan and Ian Ship. I always a slightly undersize TEV. However for the selection of a TEV, I find that using the Cool Cat of Danfoss is much better. With this you get an idea of the model, then use their Commercial Ref. Catalog to get a more accurate size.

Similar Threads

  1. Evaporator Selection
    By chooipeng in forum NH3
    Replies: 12
    Last Post: 26-09-2006, 08:11 AM
  2. TEV selection
    By Lc_shi in forum Fundamentals
    Replies: 9
    Last Post: 13-10-2005, 02:56 AM
  3. Evaporator Fan Test and Selection
    By pcle in forum Trouble Shooting
    Replies: 0
    Last Post: 18-11-2003, 03:10 AM
  4. selection of centrifugal fan
    By watana in forum Air Conditioning
    Replies: 0
    Last Post: 14-09-2003, 04:02 AM
  5. Condensor selection
    By bersaga in forum Industrial
    Replies: 4
    Last Post: 23-01-2003, 12:17 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •