    Lightbulb Chilled water fan coil unit-air leaving temp. Is 21c......?



    Dear guyes,
    We have 4 no. fan coil units for super market. (New installation and new building).unit model:American breeze,ABC-20C-C1B.CAPACITY 52TMBH(REQUIRED WATER FLOW 1O GPM).pipe size is ¾” as per manufacture recommendation. Entering water temp. Is 7c.return temp is 19c.leaving air temp is 21c and room temp is 28 c (our current ambient temp is 21c!).due to high delta ‘T’. So we checked the actual flow rate is 21 gpm for two units. As per design it is ok. Cleaned the chilled water strainer 3 times.as per design getting proper fresh air(22c supply temp) We are advised by our consultant that the ‘American breeze’ is the worst unit with their experience! But my concern due to the high delta T, there is insufficient water flow, but flow meter says getting proper water flow. Any ideas, your comment and advice would be appreciated……

    Moideen-Dubai
    Last edited by moideen; 22-12-2011 at 05:16 AM.



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    The chilled water leaving temp needs to be lower, is the load matched correctly?
    Or additional heat (unaccounted) being added?
    Last edited by Tesla; 22-12-2011 at 08:42 AM. Reason: Last line added.

  3. #3
    Join Date
    Jun 2010
    Location
    Ireland
    Posts
    168
    Rep Power
    15

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Are the flow and return water temperatures the same for the 4 units? Is the chiller serving other plant?

    Is the chilled water pipework insulated? Is there a large dehum load?

    Is there the correct air flow (what is the pressure drop of the ducting)?

  4. #4
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    3/4" line is ridiculous for 10GPM, minimum of 1" and 1.25" is better. If it is copper, I expect they won't last too long. At that rate and Dt you should be able to move 100Mbtu but the coil appears too small for the load. Just my 2 cents.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    You say that the flow rate is 21gpm for two units, do you know what is going through each individual unit?

    Manufacturers' catalogue if wanted...
    http://www.americanbreeze.com/pdf/chwfancoil.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    if ur fresh air supply is 21 is the cooling actuator closed - are you controlling off return air or actual room sensors mounted at 1.5mtr

  7. #7
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Quote Originally Posted by Tesla View Post
    The chilled water leaving temp needs to be lower, is the load matched correctly?
    Or additional heat (unaccounted) being added?
    FCU is low delta T design.leaving water temp. should be 13c.as per heat load unit is matched.
    Quote Originally Posted by RSTC View Post
    Are the flow and return water temperatures the same for the 4 units? Is the chiller serving other plant?
    Is the chilled water pipework insulated? Is there a large dehum load?

    Is there the correct air flow (what is the pressure drop of the ducting)?
    insulated.if pressure drop, i thing Delta T should be low.72 story building.mitsubishi centrifugal chiller,leaving and entering is 5.5c and 8.5c.

    Quote Originally Posted by MikeHolm View Post
    3/4" line is ridiculous for 10GPM, minimum of 1" and 1.25" is better. If it is copper, I expect they won't last too long. At that rate and Dt you should be able to move 100Mbtu but the coil appears too small for the load. Just my 2 cents.
    as per catalouge pipe size is 3/4".
    Quote Originally Posted by install monkey View Post
    if ur fresh air supply is 21 is the cooling actuator closed - are you controlling off return air or actual room sensors mounted at 1.5mtr
    now lowest ambient temp. is 15c. so fresh air is controlled.otherwise it will affect other shops and apartments. shop is in ground floor, nearest all shops and resturants(Mc donald-installed oven.....etc) getting proper cooling.


    Moideen-Dubai

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Did you correctly and thoroughly purged air from fan coils? Are they have automatic air vents?
    Last edited by nike123; 24-12-2011 at 09:11 AM.

  9. #9
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Quote Originally Posted by nike123 View Post
    Did you correctly and thoroughly purged air from fan coils? Are they have automatic air vents?
    it doesn't automatic purging line, but has common purging line, anyway my next visit to the sit will be checked.

  10. #10
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Hi
    check your piping ,are the valves 3 way or 2 way,look for crossed pipes and wrong connections ,
    the delta t you gave here corresponds most probably to crossed piping .
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  11. #11
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Quote Originally Posted by goshen View Post
    Hi
    check your piping ,are the valves 3 way or 2 way,look for crossed pipes and wrong connections ,
    the delta t you gave here corresponds most probably to crossed piping .
    good luck
    2 way valve,connection is ok.any way rechecked on monday......
    thanks to all their response
    moideen

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Quote Originally Posted by goshen View Post
    Hi
    check your piping ,are the valves 3 way or 2 way,look for crossed pipes and wrong connections ,
    the delta t you gave here corresponds most probably to crossed piping .
    good luck
    Good point, had that with half of the piping at Sharjah airport many years ago.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    is all the pipework in 3/4 or just the braches to each fan coil? is each flowrate correct to each coil?

  14. #14
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Quote Originally Posted by install monkey View Post
    is all the pipework in 3/4 or just the braches to each fan coil? is each flowrate correct to each coil?
    header 1'' and branches 3/4
    Quote Originally Posted by Brian_UK View Post
    Good point, had that with half of the piping at Sharjah airport many years ago.
    hi brian, can you please explain

  15. #15
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    So we checked the actual flow rate is 21 gpm for two units. As per design it is ok. Cleaned the chilled water strainer 3 times
    why was the strainer cleaned 3 times- was there a constant accumulation of crap? your flow rate of 21 gpm on 2 units-what was the flow rate on each unit on the system, is the main pipework lower or higher than the fan coils ? just incase there is air in the coils

  16. #16
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Hi Moideen,

    Sharjah Airport had a section of mains pipework that transferred from one side of the building to the other. In the process they managed to cross over the flow and return pipework.

    The filters were getting blocked on the wrong side and the coils and control valves were picking up all the dirt before the strainers.

    Lots of sand inside the pipework which will take years to get rid of.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Quote Originally Posted by moideen View Post
    Dear guyes, We have 4 no. fan coil units for super market. (New installation and new building).unit model:American breeze,ABC-20C-C1B.CAPACITY 52TMBH(REQUIRED WATER FLOW 1O GPM).pipe size is ¾” as per manufacture recommendation. Entering water temp. Is 7c.return temp is 19c.leaving air temp is 21c and room temp is 28 c (our current ambient temp is 21c!).due to high delta ‘T’. So we checked the actual flow rate is 21 gpm for two units. As per design it is ok. Cleaned the chilled water strainer 3 times.as per design getting proper fresh air(22c supply temp) We are advised by our consultant that the ‘American breeze’ is the worst unit with their experience! But my concern due to the high delta T, there is insufficient water flow, but flow meter says getting proper water flow. Any ideas, your comment and advice would be appreciated……

    According to your data:
    • Flow for two units is 21 gpm or 5,8 m3/h if unit is UK gpm.
    • Δt at water side of both units is 12K (19°C-7°C)
    • m=cca 5800kg
    Q=m*1,163*Δt

    Calculation say that 2 of your fan coils together are collecting 80,95 kWh of heat, and according to catalogue data, their capacity is 15 kWh each.
    So, something is probably measured wrong (flow probably) since there is no way that coils could collect that excess amount of heat.

    I would say that your actual flow is more likely 8 gpm (UK) for both units (4 gpm each).

    You should carefully measure flow and temperatures at individual units.

    How did you measured your flow? What instrument, what procedure.

    I like installing this in new installations:
    http://www.caleffi.fr/en_IT/Technica...1166/01166.pdf
    Last edited by nike123; 26-12-2011 at 03:10 PM.

  18. #18
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    I doesn't say but I wonder how they would work with Grundfos or Wilo ecm pumps that move around on the curve.

  19. #19
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Quote Originally Posted by MikeHolm View Post
    I doesn't say but I wonder how they would work with Grundfos or Wilo ecm pumps that move around on the curve.

    You should set these pumps to work with constant differential pressure.

  20. #20
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Chilled water fan coil unit-air leaving temp. Is 21c......?

    Is the water circuit a loop with a choke valve ?

    I would fit a flow meter on the return port of one of the ahu's and read the actual flow rate through the unit then take the DT.

    pictures and diagrams always help from this distance..