    Im not sure if anyone has experience of Searle evaporator , heater giving problems.
    I dont have the Model number , but its a biggish one, 3 fan motors.
    When I connected the heaters , the circuit breaker tripped, So I disconnected the heaters and left in on a forced air defrost.
    Customer adjusted stat to minus 5 c,m so I go today to a iced up coil.
    Electrician was on site so I ask him to check integrity of heaters.
    It showed 4 ohms on earth leakage test, which he said was fine.
    I connect heaters direct to circuit breaker, not via contactor and leave them on for about an hour.
    Pulling 18 amps in total.
    After an hour I hook the electrics back into contactor. This time circuit breaker trips, and in so doing takes out a fuse from the main distribution board.
    I check wires................Heater is now down to earth.
    Too late.............Electician has left site by now.
    Going back tomorrow................Why does it now show down to earth??
    Im going back tomorrow, check the wires up in the evaporator itself.
    How are these heaters connected, Ive connected them in parrallel. Might be three or four heaters embeddded within the evaporator.
    Maybe one of them is faulty. I dont know. Can only check tommmorrow.
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.
    11,025
    Re: Searle Evaporator Heaters
    Firstly, did the sparky test with a Meggar tester or a simple multimeter?
    If it was a multimeter then the earth fault may not show up.
    The heating elements are normally supported inside the sheath using a fibre of some sort. It is possible for the element to buckle and contact the outer sheath - ergo earth fault.
    You also need to confirm that the electrical connections are all dry, sounds silly but when first powered up the terminals may have been dry, defrosting then encourages water to form - possibly around the terminals. The heat keeps them dryish, you then depower the heaters but the water keep dripping onto your terminals.
    Yep, parrallel is good. Is there a problem with the contactor ?
    Apr 2001
    2,099
    27
    Prob terminals got wet Brian.............
    Ill check throughly tomorrow
    Sparky tested with a megger
    Sep 2003
    ISRAEL
    72
    4,248
    Hi Abe,
    I assume that the heaters are new, it is of a good practise to leave the heaters on for an hour or so so they will be completely dry.
    Chemi
    Sep 2005
    Granard, Ireland
    55
    43
    Have you cheked the contactor without the heaters connected, the heaters worked ok on the breaker.
    Apr 2001
    2,099
    27
    Ok sorted out problem today. Evaporator was an old one, not new........
    Had two heaters, one midway, one at bottom.
    Bottom one definately down to earth, burnt out.........
    Ive connected just one heater on at moment, adjusted the stat to cut off at 0 celcius.............
    Timer set to initiate one 30 minute defrost every six hours
    and hoping that the evaporator does not ice up
    Heater pulling around 8 amps
    11,025
    It's nice when you find the fault. It's not always nice having to fix it - but....
    May 2005
    manchester
    49
    48
    i have had this problem myself before but to keep the coil defrosting on 1 heater until the other is replaced i repositioned the evap probe into the top of the evap coil. the heaters on the searls are usally good heaters anyway so if coldroom usally work ok on 1 heater also
    Apr 2001
    Southern England
    66
    123
    Aiyub
    Suspect you have a K series cooler probably a 360. If you give Searle a call they should have the go/no go resistance and power consumption data for the heaters depends how tech you want to get. Each element used to have a part number etched on it. Searle are usualy pretty helpful and thats not just cause they used to employ me. Serial number is a big help!
    Derek
    Apr 2001
    2,099
    27
    Next time Im on site Ill have a look
    Thx
    How easy is it to remove the heater, the bottom one.........I have no space to slide it out
    Apr 2004
    UK sunny North Devon
    66
    have you checked to see if they were not 3PH heaters and you Have wired them up for 1PH, ie if you had 3 pairs at 3PH they would be rated at 110v and you left them on for over a hour they would glow in the dark
    Apr 2001
    2,099
    27
    No they are single phase
    Apr 2001
    Southern England
    66
    123
    Depend on the model and age but you can drop the drain tray and the four botton case fixings to give you some space and go in with a long (very) nose pair of pliers...
    I accept no blame for any damage.....
    Derek
    Aug 2005
    manchester
    47
    heaters on searle k 360 and large evaps like that give great difficulty in removeing heaters due to the weight of the coil which does bend ever so slightly in the middle. Sometimes is is best to drop the evap and lay upside down to remove the heaters. But if the faulty heaters have blown inside the coil it is nearly impossible to remove. might be wise to drop the evap to change the heaters if you dont have the room to change the heaters.
    :eek:
    May 2004
    64
    43
    you need at least the length of the element or you will break it on install(about 30inches)
  1. Searle Condensing Unit
    By bernard in forum Commercial
    Last Post: 01-08-2006, 10:39 PM
  2. Small Searle Cooler
    By Abe in forum Commercial
    Last Post: 27-01-2006, 06:07 AM
  3. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Last Post: 06-07-2004, 08:57 PM
  4. Searle Web-Site
    By Mark in forum Supermarket Refrigeration
    Last Post: 02-03-2004, 07:36 PM
  5. Searle Evaporator
    Last Post: 07-12-2002, 11:59 AM