    Need a correctly sized valve



    I mated a Prestcold Condensing Unit
    Model Number PR500/A0089-12-BS

    to a 20 kw evaporator, and wrongly specified a size 6 orifice for the Danfoss ext equalised expansion valve.

    The valve is overfeeding...............sending liquid all the way down the suction line, all 10 metres of it.

    I have turned the valve in and to try and reduce flow through the valve, but not having much effect, now Ive got a clump of ice around the valve body itself.

    I need to replace the size 6 orifice with the correct one. Would anyone be able to help tell me the size of orifice I need.

    I dont have a data sheet on the capacity of this condensing unit. All I can say is I am using it for a freezer application and using refrigerant R22.


    Abe


    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Need a correctly sized valve

    A rough estimate Aiyub: a PR500 is a 5 HP and gives +/-
    5 kW at -30°C, orifice 04.

    A 5HP gives at -10°C +/- 10 kW (double the HP for the kW's)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26

    Re: Need a correctly sized valve

    Thanks Peter

    Ill fit a number 4 orifice tomorrow
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

Similar Threads

  1. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  2. Scotsman commercial H2O inlet valve
    By fullcourt in forum Trouble Shooting
    Replies: 9
    Last Post: 25-04-2006, 11:41 PM
  3. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  4. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 01:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •