Results 1 to 7 of 7
  1. #1
    Mark0908's Avatar
    Mark0908 Guest

    Daikin Altherma Hydro-box Pump



    Is anyone else experiencing any issues with the circulating pump within the Daikin Altherma Hydro-Box unit, (pump failures etc)?

    Cheers



  2. #2
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Daikin Altherma Hydro-box Pump

    Hi Mark0908,

    I have experienced a few pumps failing within first year. Sounds like you have similar issues.
    Be good to hear from any Altherma installers if they too have experienced pump failures.


    Jase

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Daikin Altherma Hydro-box Pump

    We have had a couple of pump failures at the commissioning stage so have managed to replace them before handover. Most of the make used are Wilo pumps. Unfortunately if you contact Wilo to try to obtain them more quickly when out of stock at Daikin, you are advised that the particular model number is manufactured only for Daikin and not available elsewhere.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  4. #4
    Mark0908's Avatar
    Mark0908 Guest

    Re: Daikin Altherma Hydro-box Pump

    Hi Jase & hyperion,

    Thank you for your replies.

    I have had a few pump failures. A couple at commissioning and a number within the first year of installation.

    That's correct hyprion, I have contacted Wilo regarding these pumps and they are quite tight-lipped about them!

    Daikin have informed me that they have no stock of these pumps now, which has raised concern with me, and why I've asked the question.

    Thanks again,

    Mark

  5. #5
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Daikin Altherma Hydro-box Pump

    Just the help that we all need when the next breakdown is just around the corner!
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  6. #6
    Join Date
    Jan 2011
    Location
    UK
    Age
    54
    Posts
    78
    Rep Power
    14

    Re: Daikin Altherma Hydro-box Pump

    Touch wood pumps have been fine but we have had thermistors, an immersion a back-up heater a controller and a fan impacting the casing all within very short time frames from commissioning.

    No wonder Daikin's are cheap!

  7. #7
    Join Date
    May 2011
    Location
    Scotland
    Age
    57
    Posts
    11
    Rep Power
    0

    Re: Daikin Altherma Hydro-box Pump

    Hi Mark 0908,
    We have had 3 failures in 6 years.
    All series 16 system.
    Two becoming stiff on the spindle, one with winding failure.
    We have had no problem getting spares from Space Air.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •