    How hot the water is needed for heating with radiators?



    Dear all,
    I have a project with an air source heat pump water heater for the house heating with radiators. do you have any idea about what temperature does the hot water needed to run inside the radiators?



  2. #2
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: How hot the water is needed for heating with radiators?

    Air source heat pumps heat water to somewhere around 55 to 60 degrees c here.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  3. #3
    Join Date
    Jul 2011
    Location
    Greece
    Posts
    7
    Rep Power
    0

    Re: How hot the water is needed for heating with radiators?

    Quote Originally Posted by mikeref View Post
    Air source heat pumps heat water to somewhere around 55 to 60 degrees c here.
    thanks, mikeref.
    but hot water with 55 to 60 degree c for what use? house heating? sanitary hot water?

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: How hot the water is needed for heating with radiators?

    Unless you select a high temperature ASHP unit which will provide central heating water flow temperatures of between 70 and 80C, the maximum water flow temperature from an ASHP will be 55C.
    The temperature of the domestic hot water can then be adjusted upwards using an immersion heater in the hot water storage tank.
    If you are using the LT version, you will need to ensure that you radiators are suitably oversized to give the heat output required with the lower flow temperature.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  5. #5
    Join Date
    Jul 2011
    Location
    Greece
    Posts
    7
    Rep Power
    0

    Re: How hot the water is needed for heating with radiators?

    thanks hyperion.

    Now only LT version ASHP available for me. I think I will take your suggestion on LT version.
    thank you, my friends.

  6. #6
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: How hot the water is needed for heating with radiators?

    Whichever size ASHP you choose, make sure that you have sufficient water content if the radiators have TRV's fitted. If all TRV's or zone valves should close, you will need to maintain a minimum water content and flow rate to prevent lock outs on the ASHP due to low water flow.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  7. #7
    Join Date
    Dec 2011
    Location
    China
    Age
    41
    Posts
    2
    Rep Power
    0

    Re: How hot the water is needed for heating with radiators?

    Hi everyone,it is my first time to come here.Air to water heat pump can supply average 55 deg celsius hot water and max at 60 deg.If you need,you can talk to me by biz email:meeting9@heatpumpchina.com.Sorry for advertizing here.--Sam Huang

  8. #8
    Join Date
    Dec 2011
    Location
    China
    Age
    41
    Posts
    2
    Rep Power
    0

    Re: How hot the water is needed for heating with radiators?

    Hi,I'm Sam.Happy new year!

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •