Results 1 to 7 of 7
  1. #1
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    abb inverters ach550



    greetings gentlemen, i have this inverter on site, 415v input ok, inverter runs in manual start ok, but the auxillary connections are getting a 24vdc output so the remote start isnt working, is there a fuse on the board as its well wrapped and i dont want it in peices if there isnt a fuse within, ive got the install manual but it doesnt say anything helpful
    thanks



  2. #2
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: abb inverters ach550

    Try here www05.abb.com/global/scot/scot201.nsf/veritydisplay/15b3bf2d32edc615c125736f00479c05/$file/en_ach550_02_um_b_lowscreenres.pdf
    i`m not sure if the info you want is there but it might be useful in the future

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: abb inverters ach550

    HI
    it seems like you should check your wiring !!!!
    dissconnect all your inputs and check ,
    if you need the manual mail me ill send it, this is the hvac model .
    best regards
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: abb inverters ach550

    hi goshen, ive proved 415v input, disconnected the aux connections and im supposed to have 24v dc on terminal 10,but unfortunatly no joy, ive got a manual but its all about programming ,installing and no mention of any fused output.
    Quote Originally Posted by goshen View Post
    HI
    it seems like you should check your wiring !!!!
    dissconnect all your inputs and check ,
    if you need the manual mail me ill send it, this is the hvac model .
    best regards

  5. #5
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: abb inverters ach550

    I had a problem with an abb inverte. Give them a bell their tech dept is very helpful

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

  7. #7
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: abb inverters ach550

    Hi
    check the npn pnp settings on the microswitches on the drive ,
    this could be the problem ,
    or you might actully have a faulty drive .
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •