    Help needed with coolroom evaporator diagnosis please.



    How do i use a temp probe and service gauges to diagnose the gas charge in a coolroom evaporator .
    *
    If my room temp is plus 10 degrese and my thermometer probe in the coil is reading 0 degrees and my service gauges say 125 kpa or minus 27 degrees on R404 then what am i supposed to understand about the system . Is it under charged ?
    *
    *
    If my coolroom is running correctly and the room is at 1 degree then what should my thermometer in the coil read and what should my service gauges read?
    *
    thankyou

    Szarn



  2. #2
    Join Date
    Jul 2008
    Location
    England
    Age
    39
    Posts
    31
    Rep Power
    0

    Re: Help needed with coolroom evaporator diagnosis please.

    And here we go........

  3. #3
    szarn's Avatar
    szarn Guest

    Re: Help needed with coolroom evaporator diagnosis please.

    im an apprentice. im sorry this question is insulting to you so will go and ask on another site.

    thanks anyway.
    szarn

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Help needed with coolroom evaporator diagnosis please.

    Hi szarn.
    is your question from a test paper or have you been thrown in the deep end to sort out a problem?

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Help needed with coolroom evaporator diagnosis please.

    Be a test or not, you can not consider only one part of a system to solve a problem

  6. #6
    szarn's Avatar
    szarn Guest

    Re: Help needed with coolroom evaporator diagnosis please.

    Its not a test. I am aware the pressure relates to temperature. I am aware that i need 6K superheat and 3 to 5K subcooling.*

    I just seem to struggle some times when i have to attend a service call and i need to diagnose a coolroom for example.

    I have seen people using probes in the evap coil and reading their service gauges and these people seem to diagnose in seconds what takes me an hour.

    I had the feeling that i was missing something. I do not have much to do with airconditioning. I mainly do coolrooms and freezers and the odd domestic freezer for one only client.

    Szarn

  7. #7
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Help needed with coolroom evaporator diagnosis please.


    Your room is at + 10
    Your coil is at 0
    You are evaporating at -27
    And you are running R404

    That's all you can say about your system, the service gauges would also give you the condensing temperature but this wouldn't prove whether it's over or under charged either.

    Thinking about the temperatures instead of pressure is a good idea but remember that the p-t relationship only applies to a saturated liquid / vapour mix, if its 100% liquid (sub cooled) or 100% vapor (superheated) then you need to measure the pipe temperature instead.

    You mentioned sub-cooling and superheat, these readings will really help you figure out what's going on, maybe the people you've seen working have been calculating the superheat, this will tell you whether there's enough refrigerant in the evaporator and might help you work out if it's also undercharged.

    You're nearly there, it's a process of elimination.






  8. #8
    Join Date
    Nov 2003
    Location
    holland europe
    Age
    65
    Posts
    78
    Rep Power
    21

    Re: Help needed with coolroom evaporator diagnosis please.

    yes undercharged or the expansion valve is too small, or not set correct.
    computer shooter
    paul deelen
    +31653300739

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Help needed with coolroom evaporator diagnosis please.

    From these measurements we could only conclude that:
    Evaporator approach is 0°C to 27°C = 27K (high)
    Evaporator Δt is 10°C to 0°C = 10K (high)
    TD is -27°C to 10°C = 37K (high)
    Evaporator is at high load from high room temperature.
    TD is to high, but we also could have MOP TXV or suction pressure regulator.
    It gives to me indication of low air flow.
    First you should check correct air flow direction and that fan s are rotating at correct speed and that air flow is not restricted by ice formation.

    Evaporator probe could be placed where air is not flowing and therefore gives you false indication of temparature at that place.

    Always first check conditions of heat exchangers, air flows and cleanliness and then proceed with measurements.

    Check this.
    Last edited by nike123; 02-01-2012 at 12:29 PM.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Help needed with coolroom evaporator diagnosis please.

    Quote Originally Posted by szarn View Post
    If my coolroom is running correctly and the room is at 1 degree then what should my thermometer in the coil read and what should my service gauges read?
    Refrigeration (evaporator) :
    Tai-Tao = 3 to 5 K Evaporator Δt
    Tai-Te=5 to 10 K Evaporator TD. take low TD for high relative humidity
    Tao-Te=3 to 5 K Evaporator approach






    Tai - air entering temperature
    Tao -air outlet temperature
    Te -Evaporating temperature
    Twi -water entering temperature
    Two -water outlet temperature
    Tc -condensing temperature






    If cold-room temperature is 1°C then:
    Coil sensor temperature should be 3-5K lower if its placement in coil represent coil air-out temperature.
    Evaporation temperature should be 5-10K below evaporator air in (room) temperature.
    Last edited by nike123; 02-01-2012 at 11:27 PM.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Help needed with coolroom evaporator diagnosis please.

    Delete this