    Mitsubishi Pury-250YMF R22 fault code 1302



    Hi.
    Can anybody help me finding the reason for the error code 1302 appear on the Mitsubishi Pury-250YMF with R22 gas.
    In the service manual code 1302 means: High pressure abnormality
    I have changed the pressure sensor 63HS and high pressure switch 63H but the code still comes up and the compressor or fans won't come in. The pressure sensor 63HS reads 70psi so is not above high threshold.
    I did find blown F03 2A fuse on the PCB, replaced it and it has not blown again but the unit after reset comes on again with 1302 fault code. What else besides high pressure sensor and switch can cause that fault if the compressor is not running?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi Pury-250YMF R22 fault code 1302

    302
    1368
    1370
    Liquid
    side
    Intermediate
    side
    High pressure abnoramlity (BC controller)
    High pressure
    abnoramlity 2
    (Outdoor unit)
    When press. sensor detects 1kg/
    cm
    2G (0.098MPa) or less just before
    starting of operation, erro stop
    is observed with code No.
    1302
    displayed.
    When liquid side press, sensor, gas
    side pressure sensor, or intermediate
    pressure sensor detects
    30kg/cm
    2G (2.94MPa) or more, error
    stop is observed with code No.



  3. #3
    Join Date
    Jan 2008
    Location
    Newbury, Berkshire, UK
    Age
    41
    Posts
    3
    Rep Power
    0

    Re: Mitsubishi Pury-250YMF R22 fault code 1302

    Hi. Install monkey
    None of this apply. The fault is on the outdoor unit as the fault comes with the unit address, so i assume is not the BC controller. The pressure read by the sensor is 0.48MPa (70psi) so is below high pressure level of 2.94MPa and above low pressure level of 0.098MPa. Any ideas?

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi Pury-250YMF R22 fault code 1302

    have u got a service manual
    Quote Originally Posted by vippaker View Post
    Hi. Install monkey
    None of this apply. The fault is on the outdoor unit as the fault comes with the unit address, so i assume is not the BC controller. The pressure read by the sensor is 0.48MPa (70psi) so is below high pressure level of 2.94MPa and above low pressure level of 0.098MPa. Any ideas?

  5. #5
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Mitsubishi Pury-250YMF R22 fault code 1302

    Faulty check valve on compressor discharge pipe,or duff PCB.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  6. #6
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi Pury-250YMF R22 fault code 1302

    YMF outdoor units have X20 relay. The coil of the relay is in the 240v 63h high pressure safety switch circuit.
    F3 protects this 240v circuit.
    If the compressor never tries to start it may be due to x20 open circuit due to failed coil & possible cause of the blown F3 fuse.

    If the compressor does start up but trips within a few seconds with no rise in pressure suspect compressor discharge check valve failed in closed position.

    To confirm allow compressor to start. watch gauge pressure or set sw1 to display HP sensor data.
    with multi meter watch 240v on HP safety switch.
    If no rise in system high side pressure but safety switch goes open & comp stops on 1302 then discharge check valve must have failed.