Thread: Leak testing
    Jan 2010
    scotland
    9
    Leak testing
    Is being asked to leak test a system with just leak detection spray enough to satisfy the "f gas police" (they are watching ). I would have thought a working electronic leak detector would be required?.
    Oct 2006
    1,848
    15
    Re: Leak testing
    Quote Originally Posted by NB12 View Post
    You are required to use both direct and indirect methods.
    Direct is any leak detection method available and
    indirect is by running the thing and measuring temps to prove it is working correctley.
    All the best
    taz
    Jan 2010
    scotland
    9
    Re: Leak testing
    Thanks for the reply. Thought it worth the asking, the mob iv ended up at here have some questionable methods.
    44
    3,800
    38
    Re: Leak testing
    I thought you had to have an electronic leak detector and recovery machine to meet the F-Gas regs per engineer?
    Jon
    Oct 2008
    newbury
    57
    1,380
    29
    Re: Leak testing
    Direct Leak Detection
    In all situations the leak test can include checks made with one or more of three “direct” measuring
    techniques:
    1) Hand held electronic gas detector.
    2) UV sensitive detection fluid or dye in the refrigerant.
    3) Soap suds or proprietary bubble solutions.
    It is often best to use a combination of techniques e.g. an electronic detector to test a wide area and
    soap suds to identify the exact location of the leak.
    Electronic detectors need to be checked every 12 months to ensure their proper functioning. The
    sensitivity of portable gas detection devices shall be at least five grams per year.