    VRV indoor units



    Chaps

    we have got a system with 16 indoor units and an itouch. The Itouch is set all to heat 23 but 3 of the indoor units keep changing over to cool mode after 10 minutes or so

    The rooms are unoccupied so we know no one is changing them over at the local controller

    also the VAMs have been set to low but keep switching over to hi

    Is there a setting I am missing here?
    Last edited by r.bartlett; 14-12-2011 at 07:22 PM.



  2. #2
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: VRV indoor units

    1. The units that switch to cooling, check DS1-1 isn't set to ON - BS BOXES. This is a cool/heat changeover switch.
    2. The VAM units, wire a controller to P1-P2, set 17-7-02 field setting for ventilation mode on Itouch control. Then, go back to Itouch control point registration and enable ventilation mode on the group address for the VAM unit.


    Hopefully this will resolve your issues.


    Regards

  3. #3
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: VRV indoor units

    Have you checked to see if the I touch has been configured with heat/cool change over groups?

  4. #4
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: VRV indoor units

    yeah put them in change over groups. You may also find that the reason they are changing over is that the other fan coils are close to the return air sensor of the other units and the fan coils that are changing over may be getting a gut full of hot air which is giving those fan coils an incorrect return air reading and allowing them to short cycle.