    denco fault



    hi
    i really need some help please
    i am working on Denco downflow D54AV close control
    its chilling fine but it keeps alarming on klixon tripped
    any surggestion why its doing



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: denco fault

    Compressor protection !!
    Check the klixon and control module.
    Check discharge temperature , and Superheat , poor superheat leads to lack of compressor cooling.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: denco fault

    Hi Banksi.
    Sorry to be so thick!
    But are you saying the unit trips on klixon failure or continues to run but shows a Klixon alarm fault?
    Obviously one is a completely different scenario from the other.

    If it is tripping then there logically I would be a looking for a fault with the klixon.
    Which once tripped for sufficient time would reset and repeat the whole cycle again and again.

    It would be reasonable to expect the reset time required to increase and the run time to decrease.

    If the controller is showing klixon failure but it is running.
    At a guess I would be looking for a break in the relevant input circuit on the controller?

    Grizzly

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: denco fault

    sorry grizzly- dencos have electric heater banks- the overheat stats are classed as klixxons on the display screen- check the belts,filters otherwise check to see if the heaters are auto or manual reset,reset it and maybe increase the temperature deadband to prevent the heaters kicking in as frequently

  5. #5
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: denco fault

    WAY HEY
    Monkey with the sneaky curve ball.
    HAHA
    Good shout all the same.
    Want some reps??

    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: denco fault

    no ta ive got 140!! haha- bet u have a few bottles of r262 in ur shed! haha
    Quote Originally Posted by stufus View Post
    WAY HEY
    Monkey with the sneaky curve ball.
    HAHA
    Good shout all the same.
    Want some reps??

    Stu
    Last edited by install monkey; 14-12-2011 at 10:51 PM. Reason: previously told stufus to stick his offer of points in an inappropiate orifice!

  7. #7
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: denco fault

    Nice one monkey !
    Your consideration is duly noted.
    Cheers
    Stu's orifice
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: denco fault

    Thanks I'M.
    You are absolutely correct as usual.
    At least you let me down gently.
    Now you mention it, my Grey cells have kicked in enabling me to remember.
    I have come across the same on the old Sirocco and Toscana units.
    In those cases the site engineers ended up changing the errant klixons.

    It's my guess they have started to weaken with use (read disc loosing it's tempering).
    Banksyi.
    Thanks to I'M, I would recommend that you change the (Metallic disc somewhere near the Heater Banks) which has their supply cable connected to it.
    Grizzly

  9. #9
    Join Date
    Apr 2010
    Location
    Hudds
    Age
    50
    Posts
    75
    Rep Power
    15

    Re: denco fault

    Yes heater banks.

    They are 1/2 klixons located on the heater bank in case something goes wrong and the heaters overheat.

    If the airflow is there then i suspected the klixon is duff.

    Rob
    Rob Woodworth
    GEA Denco Technical Support
    rob.woodworth@geagroup.com

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: denco fault

    he's prob reset the alarm and legged it-15 minute warranty!

  11. #11
    Join Date
    Apr 2010
    Location
    Hudds
    Age
    50
    Posts
    75
    Rep Power
    15

    Re: denco fault

    The Kixon's are a auto reset switch, if they don't reset it normally means they have been strained due to excessive use.

    Please bear in mind they are the last safety switch inline so if they trip there is a airflow issue.
    Rob Woodworth
    GEA Denco Technical Support
    rob.woodworth@geagroup.com

  12. #12
    Join Date
    Aug 2010
    Location
    England
    Age
    53
    Posts
    77
    Rep Power
    16

    Re: denco fault

    if its a BETA 2 Controller, the Klixon Alarm will also trip if the Vapac Drain pump siezes and cuts the fuze of the Beta 2 board.

    unusual, but its caught a few guys out over the years.....