    Rupture Disc Gauge Problems?



    We have been annoyed with PRV vent alarms but we can't determine which relief vent is the source. I would like to install rupture disks on the PRVs. I have heard a rumor the gauges mounted on the rupture disks are problematic. Anybody have any experience with these gauges?
    Last edited by Brian_UK; 12-12-2011 at 06:13 PM. Reason: Moved to correct section



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Rupture Disc Gauge Problems?

    Quote Originally Posted by Jensen Storm View Post
    We have been annoyed with PRV vent alarms but we can't determine which relief vent is the source. I would like to install rupture disks on the PRVs. I have heard a rumor the gauges mounted on the rupture disks are problematic. Anybody have any experience with these gauges?
    Hi Jenson.
    Yes you are correct all PRV and their joints can be a pain.
    Extra care is needed when assembling them and you must pay due consideration to what refrigerant they are monitoring.

    Henry (There are other manufacturers also available) do as nice type with indicator gauges.
    So at least with these you will know which one has lifted?
    Follow the link.
    Cheers Grizzly.
    http://www.henrytech.com/catalog/2010/h20-h21.pdf

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Rupture Disc Gauge Problems?

    Quote Originally Posted by Jenson Storm View Post
    We have been annoyed with PRV vent alarms but we can't determine which relief vent is the source. ?
    Tape a small clear polythene bag over all of the PRV's. The next time one blows, it will burst (read - destroy) the poly bag over the valve outlet.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Rupture Disc Gauge Problems?

    Good tip Frank.
    I have also used a grease plug as an indicator.
    Only when the valves are piped away to atmosphere the bagging or plugging can get quite difficult.
    Cheers Grizzly

  5. #5
    Join Date
    Dec 2011
    Location
    United States
    Age
    41
    Posts
    3
    Rep Power
    0

    Re: Rupture Disc Gauge Problems?

    I am going to buy rupture disks this week and i need to know if the indicator gauges are adequate. The refrigerant is NH3 and i have heard from a couple guys in the industry that the gauges are faulty. The gauge is located after the rupture disk, so there shouldn't be any pressure on them unless the disk ruptures.

    Anybody have any problems or experience with these gauges?

    Thanks

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Rupture Disc Gauge Problems?

    Hi Jenson.
    The gauge is located after the rupture disk, so there shouldn't be any pressure on them unless the disk ruptures.
    As far as I understand if the gauge is showing pressure or has moved off its standstill peg.
    Then it is indicating a leak has occurred.
    I am not sure if you can reset them?

    Most PRV'S can be re-calibrated so I assume the "telltale" can be reset.

    You need to specify these relief valves are for ammonia and they will be of steel construction not non ferrous.
    Grizzly

  7. #7
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Rupture Disc Gauge Problems?

    I have installed rupture discs in plants that had problems with the monitors on the PRV piping leaking (NH3). Even if you change the valves out for new ones you may have a small leak. Eventually it rises to the level where it will ring an alarm. Some people put in a air fitting to blow the lines clear.
    Rupture discs simply prevent the valve from leaking. The gauge only shows that the discs have ruptured. If they have you have had a serious problem.
    They are not a bad idea on ***** systems either. You can lose a lot of expensive refrigerant from a PRV on the condensor and never know it until it is too late.

  8. #8
    Join Date
    Dec 2011
    Location
    United States
    Age
    41
    Posts
    3
    Rep Power
    0

    Re: Rupture Disc Gauge Problems?

    Quote Originally Posted by NH3LVR View Post
    Some people put in a air fitting to blow the lines clear.
    NH3LVR,

    I have blown the lines clear half a dozen times in the last month.

  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Rupture Disc Gauge Problems?

    Quote Originally Posted by Jenson Storm View Post
    NH3LVR,

    I have blown the lines clear half a dozen times in the last month.
    Then back to what you said in the first place! You need to change them there valves!
    Grizzly

  10. #10
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Rupture Disc Gauge Problems?

    Quote Originally Posted by Jenson Storm View Post
    NH3LVR,

    I have blown the lines clear half a dozen times in the last month.
    This leakage from relief valves had probably gone on for years and we did not know about it. The rupture discs solve the problem. New valves can leak a bit and it takes so little to set of the alarms.
    I would not hesitate to install them. You will have to recalibrate your sensors after you put them in. They will probably have been zeroed with some NH3 in the lines.

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Rupture Disc Gauge Problems?

    Wise words NH3LVR!

    Grizzly