    Lightbulb Vrv automatic charge method



    Hi EVERYONE,
    Today i'm just looking for a simple way to do automatic additionnal charge on new VRV RQYQ__PY1. I have on sight a 12hp with 8 indoor K units (r22) and i'm not sure about the old piping lenght...
    The installation manual is not so clear for me i'd like further more information to do it as well.
    We have a bad experience in France with these new units.
    Thanks a lot
    cool#9



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Vrv automatic charge method

    r22 vrv doesnt have auto charge function, measure pipesizes,length of each liq line and do the calc

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Vrv automatic charge method

    It's a VRVIII outdoor that allows you to reuse the original pipework from what i understand.
    But I'm not to familiar with Daikin auto charge set up ,so I'll leave it to Monkey.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Vrv automatic charge method

    RYQY refers to vrv3 heat recovery-410a if this is the case then setting mode 2 has auto charge
    item Description
    0 Digital pressure
    gauge kit display
    Used to make setting of contents to display on the digital
    pressure gauges (e.g. pressure sensors and temperature
    sensors)
    1 Cool/heat unified
    address Sets address for cool/heat unified operation.
    2 Low noise/demand
    address Address for low noise/demand operation
    3 Test operation
    settings
    Used to conduct test operation without making changes
    to the PCB and replacing the refrigerant, after the
    completion of maintenance.
    5 Indoor unit forced
    fan H
    Allows forced operation of indoor unit fan while unit is
    stopped. (H tap)
    6 Indoor unit forced
    operation Allows forced operation of indoor unit.
    8 Te setting Target evaporation temperature for cooling
    9 Tc setting Target condensation temperature for heating
    10 Defrost changeover
    setting
    Changes the temperature condition for defrost and sets to
    quick defrost or slow defrost.
    11 Sequential
    operation setting
    Sets sequential operation
    (Factory set to ON)
    12
    External low noise
    setting / Demand
    setting
    Reception of external low noise or demand signal
    16 Setting of hot water Make this setting to conduct heating operation with hot
    water heater.
    18 High static pressure
    setting
    Make this setting in the case of operating in high static
    pressure mode with diffuser duct mounted.
    (In order to mount the diffuser duct, remove the cover
    from the outdoor unit fan.)
    20
    Additional
    refrigerant charge
    operation setting
    Carries out additional refrigerant charge operation.
    21
    Refrigerant recovery/
    vacuuming mode
    setting
    Sets to refrigerant recovery or vacuuming mode.
    22 Night-time low
    noise setting
    Sets automatic nighttime low noise operation in a simple
    way.
    The operating time is based on “Starting set” and “Ending
    set”.
    25 Setting of external
    low noise level
    Sets low noise level when the low noise signal is input
    from outside.
    26
    Night-time low
    noise operation
    start setting
    Sets starting time of nighttime low noise operation.
    (Night-time low noise setting is also required.)
    27
    Night-time low
    noise operation end
    setting
    Sets ending time of nighttime low noise operation.
    (Night-time low noise setting is also required.)
    28
    Power transistor
    check mode

    Check after
    disconnection of
    compressor wires
    Used for trouble diagnosis of DC compressor. Since the
    waveform of inverter is output without wiring to the
    compressor, it is convenient to probe whether the trouble
    comes from the compressor or PCB.
    29 Capacity
    precedence setting
    If the capacity control is required, the low noise control is
    automatically released by this setting during carrying out
    low noise operation and nighttime low noise operation.
    30 Demand setting 1 Changes target value of power consumption when
    demand control 1 is input.
    32 Normal demand
    setting
    Normally enables demand control 1 without external
    input. (Effective to prevent a problem that circuit breaker
    of small capacity is shut down due to large load.)

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Vrv automatic charge method

    i thought replacement technology- meant swapping indoors and outdoor on retrofits- r22 k series units are 15yr old
    * It is possible to keep R-22 indoor units from K-series and later version It is not possible to combine old R-22 and new R-410A indoor units in one
    system due to incompatibility of communication.
    * For
    quote from sales manual-if ur spending 10k on the outdoor u may as well spend on replacing the indoors.
    Last edited by install monkey; 10-12-2011 at 10:38 PM.

  6. #6
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Vrv automatic charge method

    Hi Cool 9,

    Outdoor - furthest indoor 120m max
    Outdoor - Indoor height diff 50m max (40m when outdoor is lower than idoors)
    1st Joint - furthest indoor 40m max
    Indoor - indoor height diff 15m max
    Total piping 300m max

  7. #7
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: Vrv automatic charge method

    Ok !!! thanks for all ... just make a mistake it's a 2 pipes system not heat recovery and it's already running...
    But the guy who made the commissioning procedure didn't read the service manual before.. and now i've
    to find the mistakes because i've change the 2 compressors !!!
    I'd like more advises about the automatic charge...