    3PH Motor Current and Voltage Unbalance 10%?



    Hi Guys.
    I have allways assumed that 10% is acceptable.

    However having read the attached, I am now not so sure!

    Grizzly



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: 3PH Motor Current and Voltage Unbalance 10%?

    isnt that 10% based on all phases having the same voltage

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: 3PH Motor Current and Voltage Unbalance 10%?

    From what I have learnt, this page is fine, when currant unbalanced is more then 5%, you better check the motor bearings for exesive wear.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: 3PH Motor Current and Voltage Unbalance 10%?

    engineeringtoolbox
    Voltage Imbalance and Derating Factor in Polyphase MotorsThe efficiency of an electrical polyphase motor decreases with increased voltage imbalance.

    Sponsored Links

    Electrical motors are designed to operate with high efficiency within some variation in the electric power supplied.
    • voltage variation should not exceed +/- 10%
    • frequency variation should not exceed +/- 5%
    • combined arithmetic sum of voltage and frequency variation should not exceed 10%
    • voltage imbalance between phases should not exceed 1%
    Voltage Imbalance % Derating factor
    0 1.00
    0.5 1.00
    1.5 0.97
    2.0 0.95
    2.5 0.93
    3.0 0.89
    3.5 0.85
    4.0 0.82
    4.5 0.78
    5.0 0.76

  5. #5
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: 3PH Motor Current and Voltage Unbalance 10%?

    Hi
    as install monkey posted ,over the years these numbers have proved to be correct ,what is important is how you messure these values ,on some trane units they use voltage transformers that tend to give problematic readings after a few years of use,so in any case of suspicion for voltage or current imbalance it is crucial to use good tools ,these days that most large motors are fed via vsd ,you dont have to worry about grid imbalance .most vfds alert you when these values are approached.
    interesting related articles:
    http://www.leconsystem.com/Articles/Technical paper 1.pdf
    http://www.elongo.com/pdfs/voltages.PDF
    http://www.pge.com/includes/docs/pdfs/mybusiness/customerservice/energystatus/powerquality/voltage_unbalance_rev2.pdf
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: 3PH Motor Current and Voltage Unbalance 10%?

    Goshen
    Thanks for the input, I have saved the links for a little light reading later.
    However the last 2 links are for the same document?

    IM and Chemi.
    Thanks also guys.
    Cheers Grizzly

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: 3PH Motor Current and Voltage Unbalance 10%?

    Hi Grizzly.
    avery good post, thanks Ta

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: 3PH Motor Current and Voltage Unbalance 10%?

    Quote Originally Posted by Magoo View Post
    Hi Grizzly.
    avery good post, thanks Ta
    A pleasure my friend!
    Not to busy keeping things going then?

    Grizzly.

  9. #9
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: 3PH Motor Current and Voltage Unbalance 10%?

    Hi grizzly
    oops !!!
    best regards
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  10. #10
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: 3PH Motor Current and Voltage Unbalance 10%?

    Some 2% imbalance in voltage of a lightly loaded induction motor can lead to imbalance in current of 40%. As the load increases the current imbalance decreases.

  11. #11
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: 3PH Motor Current and Voltage Unbalance 10%?

    I've yet to see a symetrical/balanced power reading at the terminals of a motor or a dist board for that matter. Except when the power is supplied from an invertor or semi online or fully online UPS, even when its fed from a local private generator supplying a building with no UPS protection. The diverse demand on each phase will cause varying voltage readings due to single phase loads fluctuating. And if the motor windings aren't as symetrical in value as you would expect them to be or one or more windings having a low insultion reading, will cause a similiar effect.

    This is one of the reasons why you sometimes see overloads set higher than the motor rating. And sometimes bypassed altogether due to the windings being passed the stage of needing overload protection due to their condition, and just litteraly being run into the ground until they slow right down and stop and turn into heaters. And just rely on the fuses to protect the feeder cable and allowing the windings to partially melt and run into the bottom of the casing.

    An interesting link though Griz. It looks like its referring to a North American system although obviously the theory will apply on any system. If only theory and practice harmonised each other though eh.
    Last edited by chilliwilly; 17-12-2011 at 09:58 PM. Reason: missing text
    Training may be finished but experience is never complete.

  12. #12
    Join Date
    Mar 2008
    Location
    philippines
    Age
    61
    Posts
    95
    Rep Power
    17

    Re: 3PH Motor Current and Voltage Unbalance 10%?

    good day, fellow members. we also do encounter substantial voltage and current differences, and the references in this post were very informative. thanks to all members/moderators for sharing the above information/references. i always presumed that there was nothing i could do with the voltage unbalances, prior to the posts i read here. thanks again