    York Open Drive Screw Chiller



    Hi,
    Anyone ever overhaul a York 250RT screw compressor?
    Heard that after the overhaul, it will be difficult to regain back the full capacity due to tolerance out, isn't it true?



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: York Open Drive Screw Chiller

    While I have not overhauled a York screw compressor I question the statement.

    If the compressor (after rebuilding) is out of tolerance, then the rebuild would be in question.

    The capacity should not be in question, if the rotor tips and the compressor housing are in good condition. If the compressor was operated with liquid injection oil cooling, the rotor tips may have been worn down. This could result in slightly lower capacity.

    Is someone trying to sell you a new compressor instead of a rebuilt one?

  3. #3
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: York Open Drive Screw Chiller

    I have a 250RT York water cooled open drive screw chiller using R-22. One of the evaporator copper tube is cracked,chilled water finally filled the entire system up with water. Need to plugged the leaky tube, remove all water out from the expansion orifice and recommended to overhaul the compressor.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: York Open Drive Screw Chiller

    If a tube has ruptured in the chiller I would recommend you test the remaining tubes for integrity. A pressure test is the most simple method.

    However, if the one tube has ruptured it may be possible that more tubes will have the potential to leak also.

    An eddy current test will provide a reasonable method of testing the chiller (and condenser) tubes for impending leaks.

    Plugging tubes is relatively easy, but rebuilding screw compressors can be expensive. Before re-starting a rebuilt compressor on this system I would suggest the above test so that you are aware of other potential leaks.


    Here are a few links for your review:

    http://www.eddy-current.com/ecteasy.htm

    http://www.eddy-current.com/ecteasy2.htm

    http://www.asnt.org/publications/mat...ov03basics.htm

    http://www.twi.co.uk/j32k/protected/.../ksndt004.html

  5. #5
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: York Open Drive Screw Chiller

    Iceman, thank you very much for the advice. We do have an Eddy Current Set and so happened I was looking for the calibration tube this afternoon, but I failed to find it, can anyone here send me a quote for supply a set of York & Trane heat exchanger tubing for 1/2", 5/8", & 3/4" in one foor in length.

    Tq

Similar Threads

  1. York Millenium Screw Chiller
    By iceman007 in forum Industrial Compressors
    Replies: 26
    Last Post: 15-01-2011, 11:56 PM
  2. York Chiller
    By HVACGod in forum Commercial
    Replies: 12
    Last Post: 11-09-2010, 06:05 AM
  3. York Screw Oil Problem
    By tomt in forum Technical Discussions
    Replies: 10
    Last Post: 02-12-2009, 02:48 PM
  4. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  5. York process chiller repairs
    By Matt in forum Commercial
    Replies: 5
    Last Post: 23-03-2004, 11:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •