    How to determine cooling capacty



    How do I determine the cooling capacity needed for a specific application?

    I know the item I want to cool, it's two large bottles of water. Refrigerant is R-143a. The temperature I want in the fridge is 38F. So, based on the 3 variables of ambient temperature, thermal load and fridge temperature how do I determine the cooling capacity I need in Watts?

    Is the thermal load simply Q=m*cp*deltaT of the bottles of water?

    I know that to size a compressor, the cooling capacity is given for a specific temperature at the evaporator. I know that it needs to be less than the temperature I want in the cooling cabinet (38F), but how much less?



  2. #2
    Join Date
    Dec 2011
    Location
    United States
    Age
    46
    Posts
    8
    Rep Power
    0

    Re: How to determine cooling capacty

    Is the calculation simply

    Cooling Capacity (W) = Qthermal load/desire pull down time - Qheat gain through walls

    where
    Qthermal load = m*cp*deltaT

    Qheat gain through walls = h*A*deltaT+k*A/d*deltaT

    This doesn't account for the decrease in ability to cool at high ambient temperatures, so I don't think it's correct. help please!