Results 1 to 18 of 18
    Oct 2011
    ireland
    40
    29
    frosting at expansion valve.
    hey lads. what can cause frosting around the expansion valve? its a ground source heat pump
    Jul 2010
    scotland
    43
    68
    9
    Re: frosting at expansion valve.
    If you are talking about frosting round the valve and control motor, it is probably a refrigerant leak on the expansion valve, caused by the bellows cracking due to moisture and releasing refrigerant. Need to replace the expansion valve and motor, making sure to torque the motor to valve body to stop this happening again. Recover refrigerant and weigh quantity to known charge weight to prove refrigerant loss.
    Oct 2003
    56
    5,519
    28
    Brian, we install a lot of GSHP. Frosting around the valve is because your system is running below 0C. What are your running pressures and temperatures? Frosting around the valve this time of the year and so early in the heating season is strange, unless to less coils were installed.
    Oct 2003
    56
    5,519
    28
    @Refcon, why you think there's a motor? Where's the bellow on an EEV? Refrigerant loss can be found simply by verifying running pressures and temperatures without prior recovering. It perhaps was never charged correct the first time. I never depend on what others did before me.
    Aug 2009
    New Zealand
    54
    2,556
    21
    Without stating the obvious,could be that the system has just been turned on (cold water in the heating circuit)
    and the condensing pressure is just low, because of the water temp fact. The suction will follow.
    Oct 2008
    newbury
    57
    1,387
    29
    Quote Originally Posted by refcon32 View Post
    Please expand on this as I cannot follow the logic at all..
    Jul 2010
    scotland
    43
    68
    9
    Thought the expansion valve was the type that has L shaped pipework and a drive motor sits on top to operate the valve by pushing the pin in and out of valve body to control fridge flow. As on airconditioning systems. Sorry for confusion
    Quote Originally Posted by r.bartlett View Post
    Mar 2009
    KZN, South Africa
    58
    2,212
    14
    Quote Originally Posted by mad fridgie View Post
    I wonder what type of pump control this heat-pump has? Interesting point MF.
    Oct 2003
    56
    5,519
    28
    Me neither Richard
    Oct 2008
    newbury
    57
    1,387
    29
    Ok but where are the bellows on a EEV
    (as Peter asked previously?)
    Oct 2011
    ireland
    40
    29
    thanks for replies lads. just to elaborate on problem,the frosting is actually on the pipe coming from the expansion valve. i have recently done a short fgas course but am a complete novice. i have installed a lot of nibe pumps and never needed to know about the refrigeration side of them. this heat pump is a neura and the compressor is in a plastic container dropped into the lawn of a lads house. his controls are very industrial looking. when he switches on his heating the the controller registers a fault after a few minutes. when i went out to look at compressor, i noticed the frost on the pipe. the compressor can be heard running but no heat is produced.
    Oct 2007
    manchester
    44
    5,707
    have u got gauges,what running pressures are u getting. what fault code
    Oct 2008
    newbury
    57
    1,387
    29
    I thought F-Gas wasn't for complete novices..How nieve am I? :-/
    ireland
    48
    1,319
    34
    Brian
    if you're stuck i can give you a digout, pm me.
    alec
    Jul 2010
    scotland
    43
    68
    9
    The bellows are on main valve body where the output shaft of drive motor enter the valve.
    Oct 2003
    56
    5,519
    28
    A shaft seal then?
    Apr 2009
    South Africa
    43
    108
    10
    It sounds to me like the system haze a gas leak, phone a technician as u are going to break it if u do not have the experience to fix this simple problem. u will also then be sure that the system will function as designed.
    No comebacks.
    THE BEST WAY OF LEARNING IS TO DO IT YOURSELF!!!
    Jul 2010
    scotland
    43
    68
    9
    I should have a working diagram of the valve I am talking about. will look it out and put it on and all will be explained
    A shaft seal then?