    All,

    I'm looking to write a report on measuring air flow in two different circumstances

    (1) Airflow over an evaporator coil in a cold store
    (2) And airflow in an office that contains workers

    So Far i've come up with two instruments i could use (Hot Wire Annometer, and a Vane Annometer)

    My question for you is could you reccomend any other instruments that would be suitable for the job or any reccomendations on places to look for information/resources

    ~Thank you for your time

    Johnny

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Air Flow Measurement Q

    You could also use a Wilson Grid, but this is normally installed into the ductwork as a permanent fixture.
    http://www.tsi.com/Airflow-Instrumen...on-Flow-Grids/
    http://www.airflow-sp.com/PDF/Wilson-Sales-Literature-Airflow-SP.pdf



  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Air Flow Measurement Q

    Pitot static tube, duct traverse and manometer for total or branch air flows.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Air Flow Measurement Q

    Hi jonnyslim and welcome to our forum
    I did some work for an air balancing consultancy a few years ago. I would use a velocity grid for the evaporator. Flow hood for the office outlets and return grills with possibly with pitot and static pressure measurements in ducting system if required. The velocity grid is accurate where the vane annometer and hot wire annometer is slightly old hack.

  5. #5
    Join Date
    Dec 2011
    Location
    England
    Age
    33
    Posts
    2
    Rep Power
    0

    Re: Air Flow Measurement Q

    Thank you for your replies Tesla, Frank and Brian. I will reasearch these and should hopefully be able to finish my report i appreciate your time in answering my question.


    -Johnny

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •