    Dec 2011
    33
    2
    Air Flow Measurement Q
    All,
    I'm looking to write a report on measuring air flow in two different circumstances
    (1) Airflow over an evaporator coil in a cold store
    (2) And airflow in an office that contains workers
    So Far i've come up with two instruments i could use (Hot Wire Annometer, and a Vane Annometer)
    My question for you is could you reccomend any other instruments that would be suitable for the job or any reccomendations on places to look for information/resources
    ~Thank you for your time
    Johnny
    Oct 2001
    Nottingham UK
    5,668
    Re: Air Flow Measurement Q
    You could also use a Wilson Grid, but this is normally installed into the ductwork as a permanent fixture.
    http://www.tsi.com/Airflow-Instrumen...on-Flow-Grids/
    http://www.airflow-sp.com/PDF/Wilson-Sales-Literature-Airflow-SP.pdf
    11,025
    Pitot static tube, duct traverse and manometer for total or branch air flows.
    Aug 2007
    Sydney
    52
    1,083
    23
    Hi jonnyslim and welcome to our forum
    I did some work for an air balancing consultancy a few years ago. I would use a velocity grid for the evaporator. Flow hood for the office outlets and return grills with possibly with pitot and static pressure measurements in ducting system if required. The velocity grid is accurate where the vane annometer and hot wire annometer is slightly old hack.
    Dec 2011
    33
    2
    Thank you for your replies Tesla, Frank and Brian. I will reasearch these and should hopefully be able to finish my report i appreciate your time in answering my question.
    -Johnny
Tags for this Thread
