    Mitsi pury-p300yhm-a problem



    ive got a system with 13 cassettes not heating but outdoor unit running,code 66-07 in the remote controllers.any ideas please as i have no idea on mitsi kit.
    thanks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsi pury-p300yhm-a problem

    mnet probs, check all ur indoors are powered 240v including any bc boxes check ur condensers have 415v and make sure u have 30v dc on m net,then try reboot of system

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsi pury-p300yhm-a problem

    1. Error Code
    No ACK error
    2. Error definition and error detection method
    The error is detected when no acknowledgement (ACK signal) is received after the transmission. (eg. When the data is transmitted
    six times in a row with 30 seconds interval, the error is detected on the transmission side.)
    The address/attribute appeared on the display on the remote controller indicates the controller which did not provide
    the response (ACK).
    3. System configuration
    (4) Errors that are not limited to a particular system
    6607
    Error
    source address
    Error display
    Detection
    method Cause Check method and remedy
    Address
    which
    should not
    be existed
    - - (1) Although the address of ME
    remote controller has been
    changed after the group is set
    using ME remote controller,
    the indoor unit is keeping the
    memory of the previous address.
    The same symptom will
    appear for the registration with
    SC.
    Delete unnecessary information
    of non-existing address
    which some indoor units have.
    Use either of the following two
    methods for deletion.
    (2) Although the address of
    LOSSNAY has been changed
    after the interlock registration
    of LOSSNAY is made using
    ME remote controller, the indoor
    unit is keeping the memory
    of the previous address.
    1) Address deletion by ME remote
    controller
    Delete unnecessary address information
    using the manual setting
    function of ME remote
    controller. Refer to this service
    handbook "IV [2] Group Settings
    and Interlock Settings via
    the ME Remote Controller 1. (3)
    Address deletion".
    2) Deletion of connection information
    of the outdoor unit by the
    deleting switch
    Note that this switch deletes
    all the group information set
    via ME remote controller and
    all the interlock information
    of LOSSNAY and the indoor
    unit.
    ��
    Turn off the power source of
    the outdoor unit, and wait for
    5 minutes.
    ��
    Turn on the dip switch (SW2-
    2) on the outdoor unit control
    board.
    ��
    Turn on the power source of
    the outdoor unit, and wait for
    5 minutes.
    ��
    Turn off the power source of
    the outdoor unit, and wait for
    5 minutes.
    ��
    Turn off the dip switch (SW2-
    2) on the outdoor unit control
    board.
    ��
    Turn on the power source of
    the outdoor unit.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsi pury-p300yhm-a problem

    check ur e mail

  5. #5
    Join Date
    Feb 2008
    Location
    england
    Posts
    9
    Rep Power
    0

    Re: Mitsi pury-p300yhm-a problem

    Thanks a lot