Results 1 to 15 of 15
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2008
    u.a.e
    48
    412
    22
    Smile how to size swimming pool heat pump?
    hi guys,
    how to calculate the size of swimming pool heat pump?i have pool volume is 145cubic meter.our maximum outside temperature is 48c in summer.average lowest temperature is 13c.can anybody advise me what the formula is to get a size of pool heat pump.any answer would be appreciated.
    Moideen-Dubai
    Sep 2009
    Iran
    66
    672
    1
    Re: how to size swimming pool heat pump?
    Q = MxC( T2-T1)
    Q= Kcal
    M= 145X1000Li
    C = 1
    T2 = you temperature you want to reach
    T1 = 13c
    this load only for water inside pool
    you are loosing heat from surface of pool and also from walls and floor .
    in how many hours you want to heated the pool ?
    from there you get your heat pump capacity in one hours and then add 10% for safe side to that
    moideen's Avatar
    Apr 2008
    u.a.e
    48
    412
    22
    thanks your replay, as per your calculation 145000*17=2465000Kcal.is this correct. i want to heat pool 24 hour time.
    Mar 2006
    Merate (LC) - Italy
    2,549
    In UAE you don't use heat pumps for heating pools. You should use solar panels.
    moideen's Avatar
    Apr 2008
    u.a.e
    48
    412
    22
    Quote Originally Posted by NoNickName View Post
    we are not more aware solar panels for swimming pool, coul u explain.we need dual function.in summer ammbent temperature reaching up to 50c.some time goes above 50c.so need to cool pool water to 30c.
    Sep 2009
    Iran
    66
    672
    1
    so in summer you have to cool it.
    Q= 145000X1X( 48-30)=2610000 kcal at 24h
    if unit runs 16h per day (as usually we calculate in system)
    So 2.610.000 /16 = 163000 load for cooling per hours (only for cooling of water)
    Aug 2009
    New Zealand
    2,554
    26
    Sizing of pools is related to surface area (it covered or not, when not in use) , more than water volume.
    And when it comes to cooling is very complex, you need to bring ambient RH into the equation. If your pool temp is below the wet bulb temp, then moisture condensates in the pool lifting pool temp and duty.
    Sep 2009
    Iran
    66
    672
    1
    Dear Mad
    you right but as you Know when we calculate cooling load in 16 h for all pools instead of 24h from 48 c to 30c it means we go for stating duty cooling capacity not for running time capacity (in running time we have to cover as you said our loosing cooling from surface and walls + how many persons in swimming )
    you see we have a lot of factors is coming on to calculate
    I am not expert of pool designer and have not done it before,
    Aug 2009
    New Zealand
    2,554
    26
    Quote Originally Posted by mbc View Post
    Dear Mad
    got to say never had the personal pleasure of the needing to cool a pool, but a number of years ago was asked to design some machines for pools, in your neck of the woods.
    Dec 2010
    Toronto, Canada
    1,454
    I have done a lot of solar pool systems. We have heated by the plastic pool heater (http://techno-solis.com/) for example.
    In Canada the general rule is 0.5m2 of panel area to 1m2 of pool surface area for areas with no shade or high winds. This is for outdoor pools but similar for indoor pools and humidity must be taken into account, usually with a heat recovery ventilator or desiccant wheel.
    We do, sometimes, cool the overheated pools by running the system at night (but you could use the HP just for that if need be). The black sky will take heat out of the pool but you will have to determine how much panel area will fill your needs. They are pretty cheap so there is not much risk in putting in more panels.
    moideen's Avatar
    Apr 2008
    u.a.e
    48
    412
    22
    you mean 163000 kcal per hour(163000/3024=53 ton!!!),is this correct????
    Sep 2009
    Iran
    66
    672
    1
    Yes it is not too much for cooling pool with chiller with that condition
    Jul 2011
    Greece
    7
    Hi, I have an article with formula for "How to calculate the swimming pool heat pump for your pool?"
    Hope this will help you.
    moideen's Avatar
    Apr 2008
    u.a.e
    48
    412
    22
    hi mbc, i had given the same valume and details to one od the heatpump supplier in dubai who advise to install 20 ton capacity.as per your your calculation is 53 ton! entairly defferent......?
    Quote Originally Posted by MikeHolm View Post
    thanks mikeholm
    Quote Originally Posted by HPG View Post
    thanks HPG, i have to study more from ur link.if you have any model sheet used same inputs, please send me. it may help me to understand well.
    Moideen-Dubai
    Sep 2009
    Iran
    66
    672
    1
    Hi Moideen
    my calculation based on to cool only the water from ambient temperature48 to 30 in 16h not in 24h with out any loosing cool in pool (we have a lot and to calculate that we need more information as same as size of pool and material of structure in pool also surface color of pool and....) .
    as I wrote before this load is a starting load ,not running load , in running load only we have to cover our loosing load ( as I wrote before) . our design should be in high load and should cover that .
    if we forgot the pool and think we have room with your volume 145 M3 (you say 2m high) == 72.5 m2
    So about 10 m x 7 m ( length X wide ) to cool this room with out any insulation. How much we need capacity?