looking for specs
Hi just lookihg for a few specs for a gree inverter split system just acquired. model gsi 6300/0 6 kw cooling . need to know what recomended circuit breaker, size of power cable,and liquid and gas line sizes. installation manual not overly detailed. if you could help would be great
-
04-12-2011, 03:28 PM #2
Re: looking for specs
Hi Dave,
This is the English distributor if it helps.
http://www.greeuk.co.uk/
Cheers,
Andy.Health and safety first..........unless I'm in a hurry.
-
04-12-2011, 03:50 PM #3
Re: looking for specs
check the outdoor nameplate for maximum current,fit a motor rated breaker,the cable size depends on the length of run,pipesizes are determined off the size of flare nuts