panasonic cu140c51xe
Has any one out there got a service manual for the above a/c. The unit runs for 10mins and stops. No alarm codes on pannel. Only a flashing led no.5 green/yellow. Thanks.
-
03-12-2011, 11:08 AM #2
Re: panasonic cu140c51xe
sent u e mail
-
07-12-2011, 11:34 PM #3
Re: panasonic cu140c51xe
I think it is actually nine minutes, and not ten....
And I suspect it will be your indoor coil sensor....
-
08-12-2011, 10:24 AM #4
Re: panasonic cu140c51xe
thanks i will check it out.
-
08-12-2011, 01:37 PM #5
-
09-12-2011, 01:02 AM #6
Re: panasonic cu140c51xe
I thought you guy’s in WA did, don’t you charge by the minute these days J
Seriously though, there is nothing in the firmware about 10 minutes, but the closest is that if the compressor runs for 9 minutes, and the indoor coil is below 2 degrees, it cycles the compressor off, without a fault code..
-
18-12-2011, 06:56 AM #7
Re: panasonic cu140c51xe
Thanks for your help guys. Replaced the indoor coil sensor. unit is now working fine.